The spd needs a live neutral and earth, normally connected after the mainswitch in a Cu, but there’s no reason it can’t be connected before.

you’ve already put one in? Then it’ll protect both if both main switches are on
 
The main issue with SPD is the cable length.

What they are trying to stop are surges in the microsecond range and as a result all of the power is spread up in to the 100kHz+ region and so cable inductance dominates over resistance in almost all cases.

So if you have the SPD on the CU such that the cable length from supply L tap point to SPD and back to N tap point & E to MET is less than 1m (but ideally less than 0.5m) the SPD will protect loads off both CU.
 
Single phase or 3 phase?
[automerge]1601235786[/automerge]
The spd needs a live neutral and earth, normally connected after the mainswitch in a Cu, but there’s no reason it can’t be connected before.

you’ve already put one in? Then it’ll protect both if both main switches are on
As @pc1966 says there is a length of you need to be under for it to be fully effective.
 

Reply to Fitting off spd in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
515
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
754
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

What makes it a lack of space? I’d say to the customer to dismantle a cupboard or whatever to creat the space you need for the extra equipment...
Replies
1
Views
268
  • Article
The mcb used will be sized for the spd cable.
Replies
4
Views
551

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top