Fixed Appliance RCD Protection | on ElectriciansForums

Discuss Fixed Appliance RCD Protection in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jul 4, 2018
Messages
207
Solutions
1
Reaction score
338
Location
Warwickshire
Afternoon - despite a recent 18th edition pass (all but one right!) I'm having a bit of a moment whilst planning some upcoming works at our site. In reality I should wait, go home, refer to the big book and go from there. But it's playing on my mind and I can be a bit impatient. Also, I guess there may be a bit of a conversation here about existing circuits?

Situation is as thus - need to provide a spur for sign installers to install a backlit sign - all 24v LED stuff - Class 2 transformer, connected to switched fused spur.

Unbelievably (but not altogether unexpectedly), when checking how the land lay, I found a live but unused spur floating around above the suspended ceiling - an old Ashley thing, complete with smashed backbox and a bit of tape on saying "Live" (this isn't unusual in an ex-public building that has had 60 years of various companies and sub-sub-subcontractors doing reactive 'maintenance' classed works with no real records left).

So, traced the FCU - fed in old colour FP200 from a mid 90's Federal board on its own B16 - old plans indicate it used to feed a former Fire Alarm system before it was decommissioned and replaced/relocated 20 years ago. No other appliances on circuit. Zs well within. IR not yet done.

So - do I need to protect any part of this circuit with an RCD? I deduce not, as its not a socket outlet upto 32a - its a fixed appliance. And the circuit itself already exists as installed.

My brain started going down this path because really, all I'm doing is connecting an appliance - the circuit itself is already in situ.

Appreciate there's options here and the obvious thing is to shove an RCD in- source an RCBO for the board; fit an RCD in a DIN enclosure; fit one of the much debated RCD spurs ....but does it really require one? (I can't really see the risk from the appliance perspective - it's more the fixed wiring - but as I say - that already exists).

Apologies for the musing of such a small thing - but just thought I'd throw it out there
 
Afternoon - despite a recent 18th edition pass (all but one right!) I'm having a bit of a moment whilst planning some upcoming works at our site. In reality I should wait, go home, refer to the big book and go from there. But it's playing on my mind and I can be a bit impatient. Also, I guess there may be a bit of a conversation here about existing circuits?

Situation is as thus - need to provide a spur for sign installers to install a backlit sign - all 24v LED stuff - Class 2 transformer, connected to switched fused spur.

Unbelievably (but not altogether unexpectedly), when checking how the land lay, I found a live but unused spur floating around above the suspended ceiling - an old Ashley thing, complete with smashed backbox and a bit of tape on saying "Live" (this isn't unusual in an ex-public building that has had 60 years of various companies and sub-sub-subcontractors doing reactive 'maintenance' classed works with no real records left).

So, traced the FCU - fed in old colour FP200 from a mid 90's Federal board on its own B16 - old plans indicate it used to feed a former Fire Alarm system before it was decommissioned and replaced/relocated 20 years ago. No other appliances on circuit. Zs well within. IR not yet done.

So - do I need to protect any part of this circuit with an RCD? I deduce not, as its not a socket outlet upto 32a - its a fixed appliance. And the circuit itself already exists as installed.

My brain started going down this path because really, all I'm doing is connecting an appliance - the circuit itself is already in situ.

Appreciate there's options here and the obvious thing is to shove an RCD in- source an RCBO for the board; fit an RCD in a DIN enclosure; fit one of the much debated RCD spurs ....but does it really require one? (I can't really see the risk from the appliance perspective - it's more the fixed wiring - but as I say - that already exists).

Apologies for the musing of such a small thing - but just thought I'd throw it out there
After scrolling through all the answers, need to sort it yourself or get someone in who knows what they are doing, sort the situation out and make it safe, simple really if you are unsure get an expert t in PDQ.
 
I think he knows what he is doing, and it probably is already safer as he's found the breaker.
My only thought is it would be good to improve on the "floating around on suspended ceiling".
 
Sorry if I didn't make myself clear - I didn't mention anything about what I've done post finding this, as I felt the post made it incredibly obvious I'm actually qualified, competent and employed to do this job - as well as my previous contributions to the forum!

I mean if you get non-electrically competent people talking about Zs values and DIN enclosures then that's good stuff - but I thought it was clear im in the trade ?

I've obviously traced and isolated the circuit, I just didn't mention it as I assumed it was obvious I'm competent - I was just floating the idea about how I may go about reinstating it for an alternative use.
 
Presumably, it's not domestic and, as you say, it's not a socket outlet.....and I wouldn't think FP200 is in a wall less than 50mm, anyway.....is it?
From what you say, just replace the FCU and test.
 
Prysmian cable spec - 'Features and Benefits' - 'Full size CPC in direct contact with screen'!

I wasn't suggesting using the screen as a cpc but know from its construction it will provide a pretty reliable earth path in event of a fault, and whilst it isn't specifically listed in 522.6.204(i), [The list isn't all inclusive], its use isn't prohibited and is compliant with 133.5.
[ElectriciansForums.net] Fixed Appliance RCD Protection

[ElectriciansForums.net] Fixed Appliance RCD Protection
 

Reply to Fixed Appliance RCD Protection in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
444
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
ok cheers for the help lads
Replies
7
Views
719
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
963

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top