Was changing a storage heater today, I’ve used 6 spring toggles to fix it to the wall. No straps behind the wall at all, is this safe? Seemed solid when I was giving it a pull. Didn’t have any wood for fixing a pad
 
Preferably you should have at least 2 good fixings to wood, one at each end.

a good stud finder would help, or if it’s regular plasterboard, tap along the wall with your knuckle…. The hollow sound will change as you move away from/ toward a beam.
failing that, small screwdriver pushed through along a line every 40-50mm or so until you hit the woodwork…. The next beam should be 600mm away from that.
Messy, but the holes should be hidden behind the bracket.
 
Preferably you should have at least 2 good fixings to wood, one at each end.

a good stud finder would help, or if it’s regular plasterboard, tap along the wall with your knuckle…. The hollow sound will change as you move away from/ toward a beam.
failing that, small screwdriver pushed through along a line every 40-50mm or so until you hit the woodwork…. The next beam should be 600mm away from that.
Messy, but the holes should be hidden behind the bracket.

jabbed a hole right across with a driver and got nothing
 
What’s holding the wall up?

seriously. Is it a regular plasterboard wall? Dot and dab? Is it a partition wall between rooms?


when I first qualified, early 90’s, I was going round fitting storage heaters in all the council houses. Team of 8 in 4 pairs. We were given fibre rawlplugs and 2” x 10 screws. Some walls were impossible to drill that deep, others crumbled.
The type of families we were dealing with, not surprised the kids tore the heaters off the wall.
Left a screwdriver on one kitchen floor and it stuck to the grease. ?
 
Or 400mm or 450mm or any other spacing the joiner felt like using
Older properties are generally at 16in spacing
True. 600 for modern builds, but could be anything really.
OP has stated there isn’t any at all, so it doesn’t really matter in this instance
 
Should be ok if the plasterboard is in good condition. Just make sure you have the fixings at the bottom of the slotted holes on the heater. That way as the heater settles and drops down the fixing will move up along the hole rather than pull out from the wall.
If you are really worried cut the wall open and fit some supports in, it will be hidden anyway.
 
What’s holding the wall up?

seriously. Is it a regular plasterboard wall? Dot and dab? Is it a partition wall between rooms?


when I first qualified, early 90’s, I was going round fitting storage heaters in all the council houses. Team of 8 in 4 pairs. We were given fibre rawlplugs and 2” x 10 screws. Some walls were impossible to drill that deep, others crumbled.
The type of families we were dealing with, not surprised the kids tore the heaters off the wall.
Left a screwdriver on one kitchen floor and it stuck to the grease. ?
Regular plasterboard wall separating 2 rooms. Wasn’t much space behind the wall until you were through the other side into the next room. The ones that came down were held up with gyprock fixings which a thought was nuts lol!
 
Should be ok if the plasterboard is in good condition. Just make sure you have the fixings at the bottom of the slotted holes on the heater. That way as the heater settles and drops down the fixing will move up along the hole rather than pull out from the wall.
If you are really worried cut the wall open and fit some supports in, it will be hidden anyway.
Not massively worried. Previous heater was held up with gyprock fixings, gave it a good pull and wasn’t any movement from it.
 
Would not trust those things to hold any weight. (Screw in plasterboard fixings”
Seen many a simple pendant held up with a couple, just for them to drop out when someone tried to fit a shade
 
Regular plasterboard wall separating 2 rooms. Wasn’t much space behind the wall until you were through the other side into the next room. The ones that came down were held up with gyprock fixings which a thought was nuts lol!
This sounds like a paramount board wall, basically two plasterboards with an egg box type separator that puts the boards about 30mm apart
 

Reply to Fixing storage heater in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Thanks buff.
    • Friendly
    • Like
Replies
3
Views
127
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
730
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

From the front cover of the manual: Newlec Helpline: 0800 783 6909 https://www.manualslib.com/manual/3408290/Newlec-Nlsh050.html#manual I think...
Replies
1
Views
384
M
This old thread has a short video which seems to reinforce your description (see post #2) but doesn't help much...
Replies
1
Views
371

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top