Fixing to Stramit overhead !

Soulsurfer

-
Arms
Hey all, I have a flat rewire for a regular and upon cutting ceiling we have found that old stramit straw covered in cement stuff quite deep before the concrete again, anyone got any advice / ideas on method to attach slip tube to run cables in before skim again ? I can't think of much inspiration at present ! cheers.
 
Just beware that there is a straw-type substance with quite a high Asbestos content. Found lots of it in roofspaces in a school near here.
 
The only time that I have had to deal with stramit was used as internal wall partitions at regular intervals it had holes through for wiring never known it to be used on ceilings though.
 
why not re-use the existing conduit and add a cpc conductor if the conduit is not goo
Could you not use the existing conduit, or is it being removed for some reason?
one would think that, given the age of the installation, the old conduit would not serve enough points appropriate with today's needs.
 
Yep going to use the existing conduit and unfortunately can't get another singles cpc down the conduits so going to use conduit plus earth off back of the solid back boxes to accessories too and make sure well low enough.
 