Yes was just wondering if a spurred off extractor could effect my readings before I have to put new legs in
 
So that could bring the n-e down? Hopefully it is that dont really fancy putting a fresh leg in


Deffo disconnect it, but if it's just a 4" double insulated job then there isn't an earth requirement in the fan (obviously). However it will need to have been "dealt" with appropriately (the end of the cpc).

not left flapping and maybe .... Touching something :hammer:
 
I have isolated the leg thats down split the ring and put it on 2 20amp breakers so I can leave it safe till Monday!The leg thats down seems to run close to tge extractor looked inside and there is 1 x1.5 but no sign of a fcu so assumed it was part of the lighting circuit! If it has been spurred off the ring could this give me the strange readings

You need to find out if the fan is fed from the RFC or the lights its no good assuming that it is.

I know you say you are getting 0 Meg on the N/E leg of the ring but change your meter setting and test it on low ohms /K ohms to find out what reading you are getting. If it is a very low reading doing the maths will give you a bit of a clue as to where to look !!!
 
with a 0.0 MΩ reading on insulation resistance this tends to indicate that there is either a load in place or there is contact between conductors.
A load is unlikely on NE IR, unless there is a local surge protector in circuit, but then the LE would read the same as the surge protector operates.
However testing on low ohms range will give you a better idea; a near zero result there means touching conductors, a reading in ~hundreds of ohms is a load or high resistance joint.
Because the RCD does not trip the resistance would be expected to be a significant result at least above the tens of ohms range.
For a socket circuit not tripping the RCD I would be suspecting that there is still an electronic item (probably not the fan) plugged in.
 
Depending on your supply voltage, the resistance between a conductor and earth can go lower than 0.00 meg ohms before a 30ma fault current will flow and trip the RCD. At 230 volts it's 7.67 kohms :)
 
Well you need one as you have to prove the RCD is operating at the correct fault current.

That's what the 1/2x and 1 x tests prove so a ramp test isn't essential.

And an RCD doesn't operate on fault current, it operates on a current imbalance between the L and N in a DP RCD.
 

Reply to flat down neutral to earth reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
499

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top