Would you suggest flex for fixed wiring on an EICR is a C3? The client has basically run flex from one socket to a surface socket (i.e. a glorified extension lead). However I would say this is fixed wiring.

What does 521.9.1 mean where it states "only where the the relevant provisions of the regulations are met"? Does this mean CCC, installation method, overload protection etc.
 
The regulations do indeed allow flex to be used as fixed wiring as long as it’s the heavy duty type unless the risk of damage during installation is low etc etc, types of flexes are given in bs en 59565-1
For more detail see regulation 521.9.1 page 126 of bs7671.
 
Interesting timing ...........over in the plumbers forum I have just said that as far as I'm concerned boiler wiring is "control" wiring and therefore use of 5 core "flex" is perfectly acceptable......

off to my bunker now with tin hat on!

Hello Murdoch,

Thanks for your Expert opinion - I am pleased that you would be happy for Flex to be used to wire Heating System Controls / `Controls Wiring`.

Although as I mentioned Electricians carried out the wiring on my Heating systems - usually because the Builder / Customer always wanted only ONE Electrical Contractor / Electrician certifying the whole property`s Electrical Installation - and therefore the wiring was `nothing to do with me` - I still was not completely happy that `My System` had been wired correctly.

I am also pleased to see Member Dave OCD`s message describing what I described as a method that I would have liked to have seen done.

So after many Years although I had no responsibility for the wiring on most systems [since 2005] I am reassured that both methods are acceptable - "Thanks".

Regards,

Chris
 
The regulations do indeed allow flex to be used as fixed wiring as long as it’s the heavy duty type unless the risk of damage during installation is low etc etc, types of flexes are given in bs en 59565-1
For more detail see regulation 521.9.1 page 126 of bs7671.

Hello Ian1981,

Thank You very much for the information.

Would you guess that if the Flexes that I have described were `BS Heat Resistant Butyl` it would be likely to be `Good Quality` / `Heavy Duty` ?

I would never have known the specific BS / EN Numbers.

I would value your opinion please.

Regards,

Chris
 
Last edited:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Notts
Business Name
CES Midlands

Thread Information

Title
Flex for fixed wiring
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
83
Unsolved
--

Advert

Thread statistics

Created
charlie76,
Last reply from
chris murphy,
Replies
83
Views
17,015

Advert

Back
Top