Hi guys and gals.

a job that has got me second guessing my calculations. I have been asked to fot a float switch to a pump not a problem but the distance is 525m. Now there is no load on the float switch as i will be using a contactor to switch the pump Locally. So can i use a small 1.5mm 2c swa. I see no reason not as there is no load to take into account.
with the cable being so long it affects the price alot should it require a larger cable.
Thanks
 
Hi guys and gals.

a job that has got me second guessing my calculations. I have been asked to fot a float switch to a pump not a problem but the distance is 525m. Now there is no load on the float switch as i will be using a contactor to switch the pump Locally. So can i use a small 1.5mm 2c swa. I see no reason not as there is no load to take into account.
with the cable being so long it affects the price alot should it require a larger cable.
Thanks
What are your calculations
 
you need to determine the load of the contacor coil, then work out the VD for the cable selected. if within limits, OK, if not, select a bigger cable.
 
What's the purpose of the pump and float switch, why is the float so far away.?

The only thing I can think of is Spring water into a tank, then a pump in a house / building 500mtrs away controlled by the float switch, sounds like farmers idea, just run me a cable 500mtrs over there..
 
Last edited:
What's the purpose of the pump and float switch, why is the float so far away.?

The only thing I can think of is Spring water into a tank, then a pump in a house / building 500mtrs away controlled by the float switch, sounds like farmers idea, just run me a cable 500mtrs over there..
How about a solid state relay to switch the contactor,think they only draw milliamps?
S
 
so just say a 32A contactor with a 230v ac coil uses about 7va,
7/230=0.03A
according to the data sheet for a shneider contactor, voltage limits for coil are 0.8 to 1.1 x nominal
therefore for stable operation the minimum return voltage to the coil should be 230*0.8=184v

this is not a distribution or lighting circuit so volt drop is calculated on component ratings as you are designing the control system.
assuming the nominal voltage is 230v you can deal with up to 46v dropped along the length of the cable.
mV/A/m for swa 1.5 2 core is 29
or for a 0.03A load that would be a drop of 0.87mV/m
max cable length for a 46v drop would be 52.8Km

i think you should be ok at 500m in my humble opinion.
 
volt drop in the tables is already working on the assumption of a flow and return leg, at least that is what i have always assumed.
i.e. on a single phase supply cable voltage at origin is 230v
voltage at appliance may be 220v after volt drop
this is 5v dropped along the line conductor and 5v dropped along the N conductor.
i.e. in theory you should be able to measure 5v between N and E at the current using device end of the cable.
 
Good practice would be to allow for coil volts to be in the 0.8-1.1 range with the mains at its limits, reducing the available drop in the cable to around 10%, less if there is significant drop in the circuit feeding the control unit. Obviously still OK by miles using 230V, but if you wanted a lower voltage control circuit, 48V works well for a typical 7VA coil (4.6% VD) but 24V does not (19% VD). A small relay with 1-2VA coil power would be OK at 24V though.

BTW I suspect the 29mV/A/m VD figure is at 70°, so it's very slightly pessimistic as the cable will never dissipate measurable heat.
 
I try to get the facts right at least. Any literary value in the posts is a bonus and probably accidental. Think monkeys / typewriters / Shakespeare, but with techy monkeys.
 
Thanks @James and others.

yes @snowhead your not far off. Its a tank fed of a stream, to be pumped to a holding tank for cattle/sheep drinkers. Bore hole pump being used as head is 70M ish and 500M length of pipe. Pump has been trialed manually on an extension lead took around 7 minuets to reach the head and about 210L of water in pipe.
Im happy with 1.5 swa 2core not 3 as earth not required to float switch and zs wouldn't comply even with 3rd core so is rcd protected.
 

Reply to Float switch wire volt drop in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

The cable is way undersized. If the voltage drop is detrimental to the installation I would make a mention of it as volt drop generally is not...
Replies
2
Views
292
  • Question
There are two reasons for a fuse/mcb they are: 1) fault conditions - which must exist always, and be capable of operating for all points on the...
Replies
4
Views
927

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top