Hi i have been asked to install a floodlight outside a garage. There is no DB in the garage but there is a flourescent. What would i have to do to pick up a feed for the floodlight? The flourescent is the only way i can see of getting a feed.
I would be greatful for any help.
you would only be adding a light and switch to an existing lighting circuit. if a 500w flood, that's 2 more amps, so could overload MCD. Prefer to feed from socket ring/radial via FCU if possible. perhaps a low energy flood would get you out of the proverbial
The floodlght will have a PIR aswel. Could anyone please descripe the best posible way for me to do this. i am currently an apprentice so have a little experience. just want to make sure i do it right. many thanks
best way is from socket circuit,( ring or radial) through fused spur. 1. it can be isolated. 2. It's fused down to 5A. 3.It complies with regs. 4. On most PIR floods, the fused spur can be used to manually override the PIR by flicking OFF/ON
Not Quite. You MUST bring out same size cable as the socket is wired in ( usually 2.5) to your spur, then 1.5 or 1.0 from spur to flood
Reply to Floodlight being installed in the Australia area at ElectriciansForums.net
A day for sure. I recently installed an Anderson with dedicated CU. The run was a fair bit worse as I had to drop a section of ceiling and chop...
My bafflement increases. I swapped the offending light with one elsewhere on the back of the house - one of those that's on a circuit of its own...