I went and had a good look and from what I can tell, it's deffo not leading to a spur. I then went and looked at the paperwork that I have and got the details of the guy who did the testing and inspection on the place before I ended up there. Call him, sent him a pic and he said from memory its a ring, so both need to be connected, explains why they were connected initially I guess.

From a learning perspective, what would happen if only one of the T&E cables was connected and the other not?
 
From a learning perspective, what would happen if only one of the T&E cables was connected and the other not?

You would end up with two radial circuits, wired in 2.5mm, both connected to a 32A breaker... Which is not good.
 
You would end up with two radial circuits, wired in 2.5mm, both connected to a 32A breaker... Which is not good.
...and those radials wouldn't, aside through complete coincidence, be evenly split either.

If that socket is the first or last on the ring, you could easily end up (effectively) converting your ring into a single 2.5mm radial with a 32A breaker on it...
 
If that socket is the first or last on the ring, you could easily end up (effectively) converting your ring into a single 2.5mm radial with a 32A breaker on it...

That's what I basically said. You can't go pinching my waffling on this forum...
I demand payment... With cheesecake..
 
A Ring final circuit allows 2.5mm cable (which can only carry around 20A in some circumstances) to be used with a 32A MCB on a 32A circuit. This works because every socket has 2 routes back to the MCB (either way around the ring) so the current is divided between the 2. As others have said, if you creat a break in it somewhere, up to 32A could flow down one leg and via one 2.5mm cable, overloading it.

It is a wiring method not often found outside the UK, and was devised after WW2 to save copper. It is safe enough when a properly wired in a ring with sound connections, but its very easy to leave in a dangerous state if modified incorectly.
 
That's what I basically said. You can't go pinching my waffling on this forum...
I demand payment... With cheesecake..

You'll have to just live with the satisfaction of knowing I'm now hungry and wanting cheesecake, and will be in this sorry state until I can get my hands on one this evening.
 
It looks like you have
Before I moved into my flat, it had undergone a quick makeover and as part of that some wiring work was carried out including some extra sockets. I was told that under the kitchen breakfast bar there is T&E already there, it's just that the previous owner never installed a socket there but the wiring is there.

So yesterday I dived under and had a quick look. After taking electrical tape off each core, I discovered there are 2 sets T&E. I bought a 1 gang Contactum 13A floor socket and wired it in:

(a) with just one T&E attached
(b) with both T&E cables wired up together

And it works either way absolutely fine (note: I cut the T&E shorter afterwards and then took the image you see attached).

My question is whether I should go with option (a) and just tape the other core up properly or option (b)?

View attachment 48724
Attach both T&Es to the socket.
Show us a picture of the socket, so we can tell you it doesn’t comply.
 

Reply to Floor socket - 2 sets of T&E? in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Came across 3No 1ph heaters connected by 2xT&E cables from a 3phase supply on an installation whilst carrying out an EICR few years back...
Replies
9
Views
792
  • Question
Thanks for your time and opinion.
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top