I have fitted underfloor heating, using a WarmUp Wifi thermostat.
When i turn it on, the RCD trips after 5 seconds on initial turn on.
I have measured the following;
Live - Neutral - 39 Ohm (expected for size of mats)
Neutral - GND - >1M
Live - GND - ~150k
Now the L-G resistance of 150k seems unusual. I would expect either infinite or a direct short?
I did notice that the plasterer had slightly nipped one of the wires, but it seemed as the sleeving had just come off?
Any ideas? 150K is not ideal, but could it just be that the RCD isn't sufficient for the power required to power the mat?
Any help would be appreciated, would be devastated if it doesn't work, a lot of money and hard work down the drain!
sounds Like the heating mat has been damaged during installation, ideally you would be looking at insulation resistance measurements of >200M ohms between line conductors and earth
When I fit these I test straight out of box, once laid just before next stage of flooring carried, connect my monitoring device while other flooring works carried out then test again before my connection and commissioning stage
That is the way it should be done . Test at every stage and save that sickening non event.
He did not reply if the installation results were OK.
Hopefully the nick in the cable and damp plaster may be the problem.
Not normally plaster on the floor, well not withstanding those plasterers do slop it about :)
Wonder if the floor tiles ben laid? @Jamie Harper there are some companies who suggest they can locate such faults, if your floor tiles are expensive ones.
I was thinking damp plaster in the chase for the receiver lol.
I just guessed that is where the cable is nicked. :)
if it is it's only a tail and could easily be repaired.
North Wales
Business Name
NA
Flooring Tripping RCD
Electric Underfloor Heating Wiring
Jamie Harper,
Dan,
TrueNAS JBOD Storage Server
