Hi Guys

New to this whole gig, currently doing my 2330 and have got hold of a 1653B

possibly the dumbest question on this site but....

When zeroing your leads do you touch the tips together?

Thanks
 
Yep sussed that one I was just to much of a chimp to touch the leads together while doing it

new toy was worried i would short something
 
When your doing the insulation resistance test, be sure to test the meter on a known source first. The best way to do this I have found it to hold each tip in seperate hands and test, anything under a meg andf your fine. Let us know how you get on.

Rich
 
When your doing the insulation resistance test, be sure to test the meter on a known source first. The best way to do this I have found it to hold each tip in seperate hands and test, anything under a meg andf your fine. Let us know how you get on.

Rich
you sod!
 
When your doing the insulation resistance test, be sure to test the meter on a known source first. The best way to do this I have found it to hold each tip in seperate hands and test, anything under a meg andf your fine. Let us know how you get on.

Rich
Dont forget to make sure its 100% by getting them wet first, our app did it with dry hands and got funny readings
 
You will find it very hard to kill your fluke, I set fire to drills, oscilating saws and generally bugger up every tool I touch, my Fluke is the exception to the rule! (Touch wood) Bounce it like a basket ball, short it out, swing it by the leades its fine!!!!!!

For the IR test one lead in the mouth, the other in both sets of finger tips, as said confirms its working well.works best.
 
Somewhere in your Fluke box there should be a fancy piece of bent metal which Fluke provide as a device to aid nulling the Fluke leads. They call this expensive accessory the "zero adapter", it is provided because unlike most MFTs the 165xx series also require the BS1363 loop/RCD test lead to nulled before its use and the zero adapter allows easy shorting of the BS1363 plug pins. The zero adapter also has 3x4mm sockets to allow nulling of the red, black and green leads when used as prods or with croc-clips. Before the introduction of this device Fluke were getting a lot of complaints about inconsistent loop/RCD test results, caused by poor nulling or lack of nulling of the test leads.
Fluke zero adaptor (165xx) Part No. 3261925, £31 + VAT @1/2/2011
 
Last edited by a moderator:
Well after 3 years I finally past my 2330. I did however find an effective way of testing the IR on the meter. I purchased the earth spike kit for just £75 and found that if i sat on the red spike (while fully deployed) and inserted the green probe up my left nostril I was able to achive a consistant reading of around 1.5M Ohm. Thus proving I am just as thick as I ever was.

I did however work out how to use the bendy bit of metal

Shhhh dont tell anyone but i might be getting the hang of this....
 

Reply to FLUKE 1653B Zeroing the leads in the Electrical Tools and Products area at ElectriciansForums.net

Similar threads

  • Question
This lesser known technique can be used for RCBO protected circuits, allowing a high current test to be used. It's a good one to have in the bag...
Replies
13
Views
3K
  • Question
Good point, they do look a bit 6mm-ish when you mention it, and that is not going to last long enough for a D63 to trip! It might, on a good day...
Replies
7
Views
1K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

Search Electricans Forums by Tags

Tags Cloud - Most Used Words - Use them to search for topics

110v 12v 17th 17th edition 18th 18th edition 2 way 2330 2365 2391 240v 3 phase 6mm access account across adding additional advice advise after again alarm alarms always am2 amendment amp another answer anybody anyone anything appliance appliances application apply apprentice apprenticeship approved area arial armoured around assesment assessment attach aus ausie elec available basic bathroom batteries battery because become becoming becsa before being bell best better between black block blowing board boards boiler bonding book books bosch box boxes brand breaker breakers british bs7671 bsi build builder building bulb bulbs business button c&g cable cable size cables calculation calibration camera can't canada car caravan card career cctv ceiling central central heating cert certificate certificates certification certs certsure change changes changing charge charger charging cheap check cheers christmas circuit circuits clamp class code codes college combi coming commercial companies company competent complete condition conductor conductors conduit confused connect connected connecting connection connections connector connectors consumer consumer unit contact contactor content continuity contract contractor control controller conversion cooker copper core correct cost council couple course courses cover cpc cps crabtree cupboard current customer customers dead deal degrees demand design details detector device dewalt diagram difference different dimmer dimmer switch dimmers distribution diversity diy dno doing domestic domestic installer don't door double downlight downlighters downlights drill driver earth earth rod earthing east economy economy 7 ecs edition eic eicr elecsa electric electrical electrical installation electrical nvq electrical tools electrical wiring electrical work electrician electricians electricians london electricians mate electricians vans electricity electrics electriians mnchester element email emergency emergency lighting employed energy engineer engineering enough entry equipment essex every everyone exam existing experience extending extension external extra extractor extractor fan fan fans fault fault finding faulty fcu final finding fire fire alarm first fit fitted fitting fittings fixed flat flats flex flickering floor fluke fluorescent for sale forms forums found free fuse fused fused spur fuses garage garden gas generator get getting going great green grid ground gu10 guidance guide guilds hager halogen happy having heat heater heaters heating hello help help please help! hi everyone hnc hob home honeywell hot tub hours house how to ideas immersion impedance improver in london incoming induction industrial industry information infraction inside inspection inspection and testing install installation installations installed installer installers installing insulated insulation insulation resistance insurance interesting intro introduction inverter inverters isolation isolator issue issues jib jib card job jobs joining junction keeps kewtech kit kitchen knowledge lamp lamps large lead leads leakage led length lenny level level 2 level 3 light light switch lighting lighting circuit lights little live load local location loft london long looking looking for work loop low voltage ltd machine main main switch mains maintenance makita manchester manual mate max maximum mcb mcbs mcs media megger member members message metal meter meter tails meters method metrel mft might minor missing mobile module money motor mounted mounting moving multi multifunction multiple murdoch myself napit need help needed needs neutral never new new build new member newbie niceic night no earth north not uk not working notifiable number nvq off offer office old online opinions options other out outbuilding outdoor outlet outlets output outside oven overload panel panels parallel part part p passed pat pat testing people periodic person pfc phase phone pipe pir place plan plastic plate please plug plumbing advice pme point points pole position possible post posts power practical practice price prices pricing private problem problems project property protected protection protective pump pvc qualification qualifications qualified quality query question questions quick quote radial range rated rates rating rcbo rcbo's rcbos rcd rcd tripping rcd's rcds reading readings really recommend recommendations red regarding registered regs regulations relay remote repair replace replacement replacing required requirements resistance results rewire right ring ring final ring main roman roof room rose running safe safety salary sale saying scheme scotland screwfix sds second section security self self employed sensor series service services shed shock short shower simple single single phase site plan size sizing skills sky small smart smoke smoke alarms socket sockets software solar solar panel solar pv someone something sorry source south spark sparks sparky split spur spurs standard start starter starting steel still storage storage heater strange strip students stuff sub main suggestions supplier suppliers supplies supply supply to surge swa switch switched switches switching system systems t&e table tails taking terminal termostat test tested tester testers testing tests thank the forum their thermal thermostat these thing things thinking those though thought thoughts thread three three phase through time timer times tips today too tool tools trade trainee training transformer transformers trip tripped tripping trips trunking trying tt system type under underfloor underfloor heating unit units update upgrade urgent used using value values valve van vehicle video volt drop voltage voltage drop volts wall wanted warning water weeks welcome west what's whats where white wind wire wired wireless wires wiring wiring help within without work working works worth wrong wylex years zone zones

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top