I have a Fluke 1653 multi function tester and after testing on a TT system need help to ensure I am recording the correct readings from the display.
Readings are as follows :-
Main earth disconnected, Z1 (loop) selected, F1 L-PE selected and three leads connected. Green to main earth, blue to in neutral and red to in line. Test = upper display 0.40 ohms, lower display 619A. F1 L-N selected, Test = upper display 76.3 ohms, Lower display 3A.
Main earth connected, Z1 (loop) selected, F1 L-N selected, Test = upper display 26.6 ohms, lower display 9A.
Am I correct in recording Ze as 0.40 ohms, PFC as 619A and earth electrode resistance as 76.3 ohms
Are these readings acceptable and If not – where am I going wrong?
A quick reply with assistance would be appreciated as I cannot put the installation live until 100% and need to certify asap.
Thanks