Hi all,
I've been having some issues trying to fix a fluorescent light in the bathroom. Here's the steps I've taken so far after it suddenly stopped working:
1. Replaced bulb with identical spec part (Philips TL5C 40W). Let's call the original Bulb A, and the new one Bulb B.
No response when light turned on - Ballast A w/ Bulb B
2. Replaced ballast with non-equivalent but, according to product spec, compatible part. I'll call the original (Philips YZ-I40EAA T5-C) Ballast A and the new one (Philips HF-P I 22-42 PL-T/C/L/TL5C EII) Ballast B.
No response when light turned on - Ballast B w/ Bulb B
3. Bulb B fitted.
Light turned on (~0.5s delay) - Ballast B w/ Bulb A
4. Light cover refitted.
Buzzing and flickering when light turned on, then went dark - Ballast B w/ Bulb A
5. Bulb A and Bulb B both refitted several times, and connections checked. Bulb B never worked, Bulb A worked occasionally, but often would flicker and buzz. After several attempts to improve the connection, Bulb A also stopped working completely (and had some visible discolouration to the tube).
I'm now unable to get a response from anything. I've checked the condition of each item, and taken what measurements I can. Details below:
Bulb A: Has been seen to work earlier, but now showing discolouration and I can hear some debris moving around inside the tube. There are 4 pins, measuring across all combinations gives an open circuit reading.
Bulb B: Has never been seen working. No visual signs of any defect/damage. If I measure across pin combinations 1-2 and 3-4 I get readings of about 4.5 ohms. I get open circuit for all other combinations.
Ballast A: Wasn't working with either Bulb A or Bulb B previously. I haven't had a chance to re-check though, as now I have no bulbs that look like they're working. There are no visual signs of any issues on the circuit board when I open up the unit. If I measure across all 4 output pin combinations I get open circuit readings, and also when I measure from these to ground.
Ballast B: Was working earlier with Bulb A, before it blew, but not reliably (unclear if ballast problem or loose bulb fitting connection). Readings across output pin combinations and output pins to ground are all open circuit.
Does anyone have any idea what could be going on here? The new ballast did have slightly different output wiring positions, but I believe I connected these all up correctly. The only one I wasn't 100% sure of was for the 4 output pins as the diagrams/markings didn't match up too clearly between old and new, but would assume if I'd got this wrong that I would never have seen any bulb light up?
Any advice is appreciated. For now all I can think of is to just try a new ballast and bulb combination simultaneously, and hope I can return Bulb B and/or Ballast B to the shop.
EDIT: Forgot to mention, I've measured the mains input to the ballast and all looks to be as expected. I also checked continuity between the bulb pins and ballast output terminals when it was fitted to check the quality of the bulb fitting connection.
I've been having some issues trying to fix a fluorescent light in the bathroom. Here's the steps I've taken so far after it suddenly stopped working:
1. Replaced bulb with identical spec part (Philips TL5C 40W). Let's call the original Bulb A, and the new one Bulb B.
No response when light turned on - Ballast A w/ Bulb B
2. Replaced ballast with non-equivalent but, according to product spec, compatible part. I'll call the original (Philips YZ-I40EAA T5-C) Ballast A and the new one (Philips HF-P I 22-42 PL-T/C/L/TL5C EII) Ballast B.
No response when light turned on - Ballast B w/ Bulb B
3. Bulb B fitted.
Light turned on (~0.5s delay) - Ballast B w/ Bulb A
4. Light cover refitted.
Buzzing and flickering when light turned on, then went dark - Ballast B w/ Bulb A
5. Bulb A and Bulb B both refitted several times, and connections checked. Bulb B never worked, Bulb A worked occasionally, but often would flicker and buzz. After several attempts to improve the connection, Bulb A also stopped working completely (and had some visible discolouration to the tube).
I'm now unable to get a response from anything. I've checked the condition of each item, and taken what measurements I can. Details below:
Bulb A: Has been seen to work earlier, but now showing discolouration and I can hear some debris moving around inside the tube. There are 4 pins, measuring across all combinations gives an open circuit reading.
Bulb B: Has never been seen working. No visual signs of any defect/damage. If I measure across pin combinations 1-2 and 3-4 I get readings of about 4.5 ohms. I get open circuit for all other combinations.
Ballast A: Wasn't working with either Bulb A or Bulb B previously. I haven't had a chance to re-check though, as now I have no bulbs that look like they're working. There are no visual signs of any issues on the circuit board when I open up the unit. If I measure across all 4 output pin combinations I get open circuit readings, and also when I measure from these to ground.
Ballast B: Was working earlier with Bulb A, before it blew, but not reliably (unclear if ballast problem or loose bulb fitting connection). Readings across output pin combinations and output pins to ground are all open circuit.
Does anyone have any idea what could be going on here? The new ballast did have slightly different output wiring positions, but I believe I connected these all up correctly. The only one I wasn't 100% sure of was for the 4 output pins as the diagrams/markings didn't match up too clearly between old and new, but would assume if I'd got this wrong that I would never have seen any bulb light up?
Any advice is appreciated. For now all I can think of is to just try a new ballast and bulb combination simultaneously, and hope I can return Bulb B and/or Ballast B to the shop.
EDIT: Forgot to mention, I've measured the mains input to the ballast and all looks to be as expected. I also checked continuity between the bulb pins and ballast output terminals when it was fitted to check the quality of the bulb fitting connection.
Last edited: