Hi guys first time posting on here, so here is my question. I work in street lighting and I've got a fault to repair tomorrow. Just want to seee what other sparks think about it. Anyway when I disconnect a column in this certain gircuit (loop-in, loop-out) then one end of it has got juice in it even though the pillar is switched off. When I mean power, there is voltage between phase & earth , and neutral and earth although there is no voltage between phase & neutral. Also the voltage is fluctuating between about 17 &205 volts yet when I connect the circuit back together it disappears. I thnik maybe a flying earth fault although I'll know more about it tomorrow when I go to see it but I was just looking for other opinions on this fault. Cheers
 
you are getting a feed through all the other fittings on this circuit and back along the neutral. Because you haev disconnected the neutral there is no where for the voltage to go so it will be at mains level. This is why there is no potential difference between the phase (at 230v) and the Neutral (also at 230v until conected again)

As soon as you reconnect it you are allowing the Neutral potential to go to earth and therefore 0.

The fluctuation in voltage could be to do with the photocells on the fittings. are you disconnecting the CPC on the circuit when doing this. if so you are removing the earth and therefore you will get very odd readings.
 
Hi Marky thanks a lot for replying to my question. Today I went to see this fault and after a little bit of time I discovered what the problem was. At the pillar(d.b.) just at the service head cut out someone had taken a supply to feed another pillar which in turn fed 20mph school flashing signs.The problem was that they had connected the neutral for this feed directly into the neutral block for the street lighting circuits rather than into the service cable head. So that meant that when I switched off the main switch then there was no return path for this neutral which fed the other pillar.So i disconnected it and reconnected directly into the service head cut out and the problem was solved.
Thanks again for your view on this problem.
 

Reply to Flying earth fault? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Found the cause of the tripping…. Just jointed them through… all clear now. Removed the smoke detectors completely. They were due to be...
Replies
6
Views
875
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top