Started writing up the report this morning and reading through my notes.....
What would cause an rcd to fail the test at the board, passed x1/2 @ 0 and 180 fails x1 & x5, so testing directly at the rcd but it passes at 6 sockets I tested at?....had it before where it passes at the board but fails at sockets but never this way round?
 
Too sensitive? Did you try a ramp test?

If there is a fault that needs the protection, it will likely be a dodgy appliance being plugged in... so if it passes at the sockets, then all good???;)
 
Too sensitive? Did you try a ramp test?

If there is a fault that needs the protection, it will likely be a dodgy appliance being plugged in... so if it passes at the sockets, then all good???;)
Thanks littlespark that’s my reasoning, but these things keep me awake at night ?.....I’ll be honest I didn’t ramp test, with regards coding would you pass or FI?
 
I’ve put FI, no not been asked to do remedials yet but I suspect I will be......to the best of my knowledge they were all disconnected,big issue with low IR as well, the place is a shambles with sockets wired from light circuits and all sorts....
 
There are somes brands of rcbo that will not trip if tested at the board, you have to have a bit of distance for it to work (not much, a socket by the DB is normally fine)
The MEM2000 module range is one that springs to mind.
Just note it somewhere that this is a known idiosyncrasy of these rcbo's
 
There are somes brands of rcbo that will not trip if tested at the board, you have to have a bit of distance for it to work (not much, a socket by the DB is normally fine)
The MEM2000 module range is one that springs to mind.
Just note it somewhere that this is a known idiosyncrasy of these rcbo's
BG board 17th
[automerge]1575810378[/automerge]
What do you mean it fails? What readings did you get? Or did it not trip at all?
X1/2 @ 0 >2000. Pass
X1/2 @ 180 >2000. Pass

X1 @ 0 > 300. Fail
X1 @ 180 > 300. Fail

X5 @ 0 > 40. Fail
X5 @ 180 > 40. Fail
 
Last edited:

Reply to Following on from eicr thread.. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Promised a photo…. Remember, this was working…. And they managed to move in without hitting it…
    • Like
Replies
4
Views
363
That is very cool. It would be the end user software that would make that the absolute king.
    • Winner
    • Like
    • Informative
Replies
1
Views
481

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top