Started writing up the report this morning and reading through my notes.....
What would cause an rcd to fail the test at the board, passed x1/2 @ 0 and 180 fails x1 & x5, so testing directly at the rcd but it passes at 6 sockets I tested at?....had it before where it passes at the board but fails at sockets but never this way round?
 
Too sensitive? Did you try a ramp test?

If there is a fault that needs the protection, it will likely be a dodgy appliance being plugged in... so if it passes at the sockets, then all good???;)
 
Too sensitive? Did you try a ramp test?

If there is a fault that needs the protection, it will likely be a dodgy appliance being plugged in... so if it passes at the sockets, then all good???;)
Thanks littlespark that’s my reasoning, but these things keep me awake at night ?.....I’ll be honest I didn’t ramp test, with regards coding would you pass or FI?
 
FI.
If you’re asked to do the remedials.

Were all loads disconnected when you did the tests? The rcd is probably fine, just over sensitive but within design specs.
 
I’ve put FI, no not been asked to do remedials yet but I suspect I will be......to the best of my knowledge they were all disconnected,big issue with low IR as well, the place is a shambles with sockets wired from light circuits and all sorts....
 
There are somes brands of rcbo that will not trip if tested at the board, you have to have a bit of distance for it to work (not much, a socket by the DB is normally fine)
The MEM2000 module range is one that springs to mind.
Just note it somewhere that this is a known idiosyncrasy of these rcbo's
 
There are somes brands of rcbo that will not trip if tested at the board, you have to have a bit of distance for it to work (not much, a socket by the DB is normally fine)
The MEM2000 module range is one that springs to mind.
Just note it somewhere that this is a known idiosyncrasy of these rcbo's
BG board 17th
[automerge]1575810378[/automerge]
What do you mean it fails? What readings did you get? Or did it not trip at all?
X1/2 @ 0 >2000. Pass
X1/2 @ 180 >2000. Pass

X1 @ 0 > 300. Fail
X1 @ 180 > 300. Fail

X5 @ 0 > 40. Fail
X5 @ 180 > 40. Fail
 
Last edited:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Baddegg

Esteemed
Arms
Supporter
Patron
-
Joined
Location
Southsea
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
If other, please explain
?

Thread Information

Title
Following on from eicr thread..
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11
Unsolved
--

Advert

Thread statistics

Created
Baddegg,
Last reply from
Ian1981,
Replies
11
Views
1,561

Advert

Back
Top