Form 4 - Overcurrent Device - What to put down | on ElectriciansForums

Discuss Form 4 - Overcurrent Device - What to put down in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

C

chrisgc

Hi

On the form 4 - in the brb - in the box entitled:

Overcurrent Device 4 Short-Circuit Capacity: ........kA

What is that referring to?

Is it the RCD in the cu?

Just wondering as this box is above the sub headings of type and rating - which I know are for the circuits individual breakers.

Is the Overcurrent short capacity box for the RCD of the CU?

If it is what do I put down if only half the circuits in the cu are protected by a rcd?
 
overcurrent device is the MCB and the s/c capacity is usually 6kA. found on side of MCB as 6000
 
The S/C rating is also on the front of the breaker in an oblong box, it will say 6000 or 10000, this is the short circuit current rating that you require. Just in case you are not aware, this figure must be at or above the PSCC of the installation you are fitting it to.
Most domestic applications will be below 6kA.
 
overcurrent device is the MCB and the s/c capacity is usually 6kA. found on side of MCB as 6000

If its for the MCB's on the circuit (obviously more than one in the cu) and Form 4 enables you to have different circuits listed (down the side of the form) on the sheet and the MCB's are different - thus different ratings - in the CU how does the box titled --Overcurrent Device 4 Short Circuit Capacity ........kA (which is above the Type and Rating headers)-- cover all the MCB's on in the CU??

Also dont think I can see the ratings etc as the CU i have in my house has, circuit breakers like this: NB30 30a - type 2 240v on the front of them.

So a little confused and thought that the part of the form I am on about would be different for different cb's.
 
sounds like the older type plug in MCB's used to replace rewireable fuses e.g.wylex. if i rem. correct the s/c capacity was 3kA, stamped on side of MCB as 3000 in a box
 
It can be a pain in the rear with some of the older ones as they were only stamped on the side. Dont think Ive had a domestic with PSCC above about 2.5kA. End of the day mate, its your signature on the sheet, and you are going to have to look. Power off, busbar off and ping them out 1 at a time.
 
sounds like the older type plug in MCB's used to replace rewireable fuses e.g.wylex. if i rem. correct the s/c capacity was 3kA, stamped on side of MCB as 3000 in a box

Just had a search and yes older type.

So the box on Form 4 - I still am unclear what I put as its at the very top of the column and appears as though it would cover all the Cb's in the CU??? Any help please?
 
Last edited by a moderator:
whatever the S/C rating is on each MCB, in each box alongside the type, rating, etc. should be same for each one
 
If it is a type 1,2,3 or 4 then it's a BS3871 and can have a s/c capacity anywhere from 2-10 kA.

Remember, in a domestic situation on a consumer unit to BS60439-3 you can rely on the s/c capacity of the DNO fuse which is taken to be 16kA.
 
If it is a type 1,2,3 or 4 then it's a BS3871 and can have a s/c capacity anywhere from 2-10 kA.

Remember, in a domestic situation on a consumer unit to BS60439-3 you can rely on the s/c capacity of the DNO fuse which is taken to be 16kA.

This is what I was told by an assessor.

I originally thought it was the Short Circuit Capacity of the MCBs that was recorded in this box - but he said it wasn't, it's the rating of the cutout.....e.g. 16 KA
 
This is what I was told by an assessor.

I originally thought it was the Short Circuit Capacity of the MCBs that was recorded in this box - but he said it wasn't, it's the rating of the cutout.....e.g. 16 KA

WayneL

Where on the cutout do you find that info????
 
The information is on the fuse itself but of course you can't see it because it's sealed.

Then again, you could just isolate all load, cut the seal, remove the fuse, record the details and put everything back neatly but that would be illegal.;)
 

Reply to Form 4 - Overcurrent Device - What to put down in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
813

Similar threads

Well yes obviously, but if the transformer is indoors and your lights are 50m down the garden then it's very easy to need pretty big cables at...
    • Like
2 3
Replies
42
Views
2K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
996

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top