here's one I did earlier!View attachment 12609 Not the best I've ever done but the only photie I've got to hand.
labels went on later before anyone comments!
Middle set of tails go to dedicated CU. Right hand tails (as we look at it) go to main CU

Moggy, make sure you don't strip the outer sheath of the tails outside of the henley block otherwise you have a single insulated conductor with no mechanical protection outside of an enclosure which would warrant a defect code on an EICR.
 
HEY TC,

good pic! tails are undersized for 100amp suppliers fuse

The 20A MCB within the 2 way consumer unit would provide overload protection for the 16mm2 tails so not an issue though connecting before the suppliers meter is a serious no-no!
My 2 way solar CU is supplied with 10mm2 tails and that's not an issue either.

Absolute shocking job though. I'm just amazed somebody could actually carry out an installation like that and not give it a second thought :(
 
I think I have spotted another fault here chaps, they have brought the Earth in from the array, so bringing a potential into the equipmental zone, it should be on its own Earth spike, unless there are velux windows of course, which I doubt. Your thoughts?
I did not spot the RCD though, sorry.
12633d1338387698-non-solar-guy-does-look-ok-solar-arangement-012.jpg
 
All looks like cheap tat as well, probably won't last more than a few years!

Think that's the roughest solar electrical install i've seen, I wonder what the roof work is like...
 
All looks like cheap tat as well, probably won't last more than a few years!

Think that's the roughest solar electrical install i've seen, I wonder what the roof work is like...

they keep popping up on this forum, i reckon there hundreds out their like this one and its only time before we all start picking up repair work for mis sized inverters, poor wiring, panels slipping. The trouble with that install also is were was the persons pride? who in the right mind leaves a job like that, yes ok im not proud of all my jobs, but even in my early days i wouldnt leave anything like that!
 
Moggy, make sure you don't strip the outer sheath of the tails outside of the henley block otherwise you have a single insulated conductor with no mechanical protection outside of an enclosure which would warrant a defect code on an EICR.

Hey Gaz?

Does that include all tails in and out of the meter and main head too? As 95% of the instals i go to obviously dont now comply to the new EICR.
So?
Does that mean i have to make all necessary changes to the tails to make the instal/electrics comply?

Thanks

Fiardor
 
It's always been the case that you can't have a single insulated conductor outside of an enclosure or containment but you're right, there's many installs out there with that issue and the DNO are more guilty than most, especially with their meter terminations. Maybe that's where the habit has come from?
If you're carrying out an EICR then just report and code them appropriately. No need to make any changes there and then, only if the customer chooses to have the defects rectified though the meter terminations are obviously the DNO's responsibility. You can still note them on your EICR though.
 
It's always been the case that you can't have a single insulated conductor outside of an enclosure or containment but you're right, there's many installs out there with that issue and the DNO are more guilty than most, especially with their meter terminations. Maybe that's where the habit has come from?
If you're carrying out an EICR then just report and code them appropriately. No need to make any changes there and then, only if the customer chooses to have the defects rectified though the meter terminations are obviously the DNO's responsibility. You can still note them on your EICR though.

Duly noted thanks Gaz

And will from now on adhere to the new EICR. (mostly) LOL
 
I think tails are undersized for 100 amp suppliers fuse

If there's a 20A MCB in the 2 way CU then how can the tails be subjected to an overload greater than the rating of the MCB?
In other words, the MCB is your overload protection and the tails are fine.

Think of an 800A busbar chamber with a few 32A switch fuse isolators fed from it. Would you expect conductors rated at 800A to be terminated into the 32A switch fuse?
 
If there's a 20A MCB in the 2 way CU then how can the tails be subjected to an overload greater than the rating of the MCB?
In other words, the MCB is your overload protection and the tails are fine.

Think of an 800A busbar chamber with a few 32A switch fuse isolators fed from it. Would you expect conductors rated at 800A to be terminated into the 32A switch fuse?
If the RCD short circuited then the prospective fault current could be thousands of Amps.
Agree to a point about a busbar chamber but the small tails would or should be mechanically protected.
 
They are mechanically protected - by their outer sheath. No other protection needed, subject to environment.
Many thousands of amps would be great for fast breaking of a protective device that's suitably rated to break the fault current without destroying itself.
 
yes, it will only have electricity he is using pass through it. the excess will go off to the grid so I'm not right in saying he will be charged for everything he generates. As you say, just no reduction in his bill!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Top Cat

Arms
-
Joined
Location
Gloucester

Thread Information

Title
From a non solar guy, does this look OK
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
93

Advert

Thread statistics

Created
Top Cat,
Last reply from
Dan,
Replies
93
Views
11,883

Advert