Here’s my take on this:
12x 250W Sanyo panels in one string.
Sun comes up. One panel is shaded by the chimney, so its bypass diodes/circuits are active, with only eleven panels actually functioning. This would be especially true if installers had not appreciated the way the bypass diodes are laid out on a given panel.
Inverter tracks up and down the voltages on startup andfinds the optimum for the 11 unshaded panels – the optimum (Vmp) being about 34Volts.
11 panels at 34Volts, in one string, gives 374V.
The inverter sets up for harvesting at 374V and the system then happily hums along at 374V, with minor checks a few volts either side, tosee if there’s a slightly better voltage to extract maximum power.
Then a second panel also gets shaded by the moving shadow ofthe chimney, so we have two shaded panels. The inverter then tries to run the remaining ten panels at 374V. This bumps up each panel’s voltage to 37.4V,dropping off the end of the voltage: efficiency curve, resulting in inferior efficicency.
12x 250W Sanyo panels in one string.
Sun comes up. One panel is shaded by the chimney, so its bypass diodes/circuits are active, with only eleven panels actually functioning. This would be especially true if installers had not appreciated the way the bypass diodes are laid out on a given panel.
Inverter tracks up and down the voltages on startup andfinds the optimum for the 11 unshaded panels – the optimum (Vmp) being about 34Volts.
11 panels at 34Volts, in one string, gives 374V.
The inverter sets up for harvesting at 374V and the system then happily hums along at 374V, with minor checks a few volts either side, tosee if there’s a slightly better voltage to extract maximum power.
Then a second panel also gets shaded by the moving shadow ofthe chimney, so we have two shaded panels. The inverter then tries to run the remaining ten panels at 374V. This bumps up each panel’s voltage to 37.4V,dropping off the end of the voltage: efficiency curve, resulting in inferior efficicency.