Hi there
Any help most appreciated
According to the operational manual for the fronius IG TL 3.6 it has an RCMU to protect against residual DC currents. so a B type RCD is not required, It then goes on to say if an external RCD is required due to local regulations then a type B 100mA RCD should be fitted.. Does this mean if it is a TT installation it must have a seperate type B RCD????
Any help most appreciated
According to the operational manual for the fronius IG TL 3.6 it has an RCMU to protect against residual DC currents. so a B type RCD is not required, It then goes on to say if an external RCD is required due to local regulations then a type B 100mA RCD should be fitted.. Does this mean if it is a TT installation it must have a seperate type B RCD????