Evening all,

Have been asked to wire one of these into a heating system that has no separate control (or valves) for HW & CH. Customer is going to be away and wants it wiring in to allow the heating to only come on when the temp drops to keep pipes etc from freezing.


However I just want to make sure I have this right as not wired one in before.

I am assuming I just connect this to the perm L & N and call for heat in the control centre? If he switches the heating off at the usual timer control panel, will this still kick in and turn the heating on once the temp drops below the set value? The instructions just say L, N and terminal 3 call for heat.

Thanks

Carl
 
I would take the live feed from the input of the timer relay, (assuming it is 230v) then the output of the frost stat back to the call for heat input that the room stat feeds into.
basically you are creating a circuit that bypasses all timers and thermostats .
 
I am assuming I just connect this to the perm L & N and call for heat in the control centre? If he switches the heating off at the usual timer control panel, will this still kick in and turn the heating on once the temp drops below the set value? The instructions just say L, N and terminal 3 call for heat.
Yep. Exactly as you describe. (Get some 4 core flex from Screwfix)

Funnily enough I did a frost stat today, I hope your one goes better!

In my case it was a freestanding oil fired Bosch Worcester and there were frost stat connections on the main PCB. The old frost stat had become damaged and had been removed by someone else, who put all the connections in wagos and then put them in a wago box. So I assumed that joining the brown and the black sleeved brown would fire the boiler. The problem was that it didn't!

I'd been hoping to avoid opening up a DIN rail box on the wall containing a contactor and working out what was going on, but I had to dive in. In this case there was also a pipe stat in series, so the combination of very cold room and cold pipes would fire the boiler until either pipes reached 30 or the frost stat reached 3.
Eventually I worked out that the N to the coil was connected to nothing, and then in turn worked out that whoever fitted the nest had thought it was surplus to requirements.
Then to cap it all, when I powered up again the flipping nest wouldn't reconnect, long story short was that it hadn't been charging and was virtually flat, but I messed around for 40 minutes before realising this was the problem.
I thought this was a 30 minute job - I was there 2.5 hours!
 
I prefer to have them as a 5 degree room stat. then it puts enough heat into the building to prevent other pipes like hot and cold domestic water from freezing.
If the boiler is inside this is what I do too.

The recent one I did had the boiler in an outbuilding so the room stat / pipe stat combo made sense.

Incidentally is there a good reason that I'm missing why a relay was required to close the frost stat terminals on the boiler, coil fed by the frost stat and pipe stat in series? I've never seen that before. At first I wondered if it was a clever time delay relay but it wasn't.
 

Reply to Frost Thermostat wiring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

So much for trying to steer this back on track.
2 3
Replies
31
Views
985
  • Question
Update... I wired up my first heating system today! Thanks to all the help in this thread, (and the initial thread) I was completely prepared...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top