Mattyi26

Hi All,

Not posted on here for a few years! I have a question that i hope someone can clarify.

I need help understanding the differences between a full cert and a minor, correct me if im wrong a minor is for jobs that are non notifiable and full for special locations and notifiable works. So if i carry out both notifiable works and minor do i fill out both?
Can i do it any other way?

I recently joined Stroma and in the process of setting up my e-cert software so if anyone can tell me what they think of it?, Ihave done 2 jobs since registering which have both been consumer unit upgrades to 17th amend 3 and have used the generic IET certs hand written But How do i fill this out if just doing for example;

Adding 1 extra circuit in a special location;

Full cert with all 5 pages filled out? With the page schedule of test results only containing the 1 extra circuit i have added? How far do i go with the check sheets? Everything or anything that does not comply to current regs/amendment do i record on it?

If anyone can explain how they do it regarding different types of jobs?

Hope ive explained myself properly but cant find a simple answer on this!

Thanks in advance

Matt
 
Is that domestic or commercial? And where abouts are you, i suppose pricing differs around the country. I only have 4-5 spark mates and i think the general price range for us is consistant at 180-260 depending on what exactly needs doing, had a few conversations about pricing etc. i need to start upping prices just for the new aches and pains that seem to be appearing everyday lol
I have only just noticed this after enjoying the Easter break, and I have a feeling it might have slipped under the radar. ÂŁ180 to ÂŁ260 for a board change??? Are you fking mental or something? No wonder this industry is in a mess, what do you think charging that amount is going to achieve? Do you do the job properly?? Certs? proper testing? Proper workmanship? Proper evaluation of the other factors involved? This is a joke surely??? I notice you have no quals in your profile, are you a proper sparky or a quick in-out yeee-haaaa?
 
Last edited:
I have only just noticed this after enjoying the Easter break, and I have a feeling it might have slipped under the radar. ÂŁ180 to ÂŁ260 for a board change??? Are you fking mental or something? No wonder this industry is in a mess, what do you think charging that amount is going to achieve? Do you do the job properly?? Certs? proper testing? Proper workmanship? Proper evaluation of the other factors involved? This is a joke surely??? I notice you have no quals in your profile, are you a proper sparky or a quick in-out yeee-haaaa?

what are you on about? I think you need to get down from that shire of a horse you're on son.
1) no my mental health is perfectly fine so i believe.
2)the industry is a mess because im charging that amount for a days work and not because we have complete arse about face ambassadors for the industry that charge us extortionate amounts every three years for another course or another set of books? Good thinking.
3) no i leave all fuxking wires hanging out the front and leave it. Oh and i purposely make sure the board isnt IP rated to IPx4 but it doesnt matter the tails arent terminated anyway, they're hanging out the front with the rest of the curcuit conductors, but its ok i changed the unit like the customer asked... And as for certification, Bin days are every two weeks up here now so id rather do the customer a favour and keep it all in the van.
4) posting qualifications on a public forum, i have no objections to the people that have but id personally prefere not to, is that a problem? I know what i've got, my college tutors know what ive got, the old on-site assessors know what ive got, even the JIB know what i've got, why must i post it publicly?
5) yes i do; do quite a good yee-haa although im no cowboy.

My post was quite misleading in the respect that i didnt put labour only, but if you think i can supply, fit and sign off a full cu change fpr ÂŁ180 then please ask yourself those questions you just asked me. If you were unsure then juat type out, and ASK like what the other member did before you. Slipped under the radar? Ha! Like i said, climb down from that horse.

i do hope you enjoyed your Easter break.
 
what are you on about? I think you need to get down from that shire of a horse you're on son.
1) no my mental health is perfectly fine so i believe.
2)the industry is a mess because im charging that amount for a days work and not because we have complete arse about face ambassadors for the industry that charge us extortionate amounts every three years for another course or another set of books? Good thinking.
3) no i leave all fuxking wires hanging out the front and leave it. Oh and i purposely make sure the board isnt IP rated to IPx4 but it doesnt matter the tails arent terminated anyway, they're hanging out the front with the rest of the curcuit conductors, but its ok i changed the unit like the customer asked... And as for certification, Bin days are every two weeks up here now so id rather do the customer a favour and keep it all in the van.
4) posting qualifications on a public forum, i have no objections to the people that have but id personally prefere not to, is that a problem? I know what i've got, my college tutors know what ive got, the old on-site assessors know what ive got, even the JIB know what i've got, why must i post it publicly?
5) yes i do; do quite a good yee-haa although im no cowboy.

My post was quite misleading in the respect that i didnt put labour only, but if you think i can supply, fit and sign off a full cu change fpr ÂŁ180 then please ask yourself those questions you just asked me. If you were unsure then juat type out, and ASK like what the other member did before you. Slipped under the radar? Ha! Like i said, climb down from that horse.

i do hope you enjoyed your Easter break.

Yes, you should have stated 'labour only' if that's what you meant. Daz
 
what are you on about? I think you need to get down from that shire of a horse you're on son.
1) no my mental health is perfectly fine so i believe.
2)the industry is a mess because im charging that amount for a days work and not because we have complete arse about face ambassadors for the industry that charge us extortionate amounts every three years for another course or another set of books? Good thinking.
3) no i leave all fuxking wires hanging out the front and leave it. Oh and i purposely make sure the board isnt IP rated to IPx4 but it doesnt matter the tails arent terminated anyway, they're hanging out the front with the rest of the curcuit conductors, but its ok i changed the unit like the customer asked... And as for certification, Bin days are every two weeks up here now so id rather do the customer a favour and keep it all in the van.
4) posting qualifications on a public forum, i have no objections to the people that have but id personally prefere not to, is that a problem? I know what i've got, my college tutors know what ive got, the old on-site assessors know what ive got, even the JIB know what i've got, why must i post it publicly?
5) yes i do; do quite a good yee-haa although im no cowboy.

My post was quite misleading in the respect that i didnt put labour only, but if you think i can supply, fit and sign off a full cu change fpr ÂŁ180 then please ask yourself those questions you just asked me. If you were unsure then juat type out, and ASK like what the other member did before you. Slipped under the radar? Ha! Like i said, climb down from that horse.

i do hope you enjoyed your Easter break.
If you don't have any proper quals, then just say so, no need to go off on one, SON. You are correct, your post obviously was misleading, so try and be a bit more accurate in figure. Hope your CU changes are better eh? And yes I Had a great Easter break ta.
 
If you don't have any proper quals, then just say so, no need to go off on one, SON. You are correct, your post obviously was misleading, so try and be a bit more accurate in figure. Hope your CU changes are better eh? And yes I Had a great Easter break ta.

and go on, what is your take on proper quals? still on that high horse i see, maybe your mrs could buy you a comfortable saddle? Maybe a double for you and that big arse ego.
 
and go on, what is your take on proper quals? still on that high horse i see, maybe your mrs could buy you a comfortable saddle? Maybe a double for you and that big arse ego.

Without any clue as to your qualifications, and it doesn't have to be specific just saying that you served an apprenticeship in this trade would do (if you have), then we only have your previous posts to base an opinion of your ability on.
Looking at your posts on electrical matters then it's easy to see why people are sceptical of your knowledge and ability
 
Without any clue as to your qualifications, and it doesn't have to be specific just saying that you served an apprenticeship in this trade would do (if you have), then we only have your previous posts to base an opinion of your ability on.
Looking at your posts on electrical matters then it's easy to see why people are sceptical of your knowledge and ability

I understand that hence have hesitantly put them on, and before anyone points out i know im not as qualified as some, but i am JIB recognised if i bothered to renew my ecs.

can i ask which posts you're refering to?
 
I understand that hence have hesitantly put them on, and before anyone points out i know im not as qualified as some, but i am JIB recognised if i bothered to renew my ecs.

can i ask which posts you're refering to?

Ive never yet bothered with the JIB, and I'm not sure I'd get a very good grade even if I did.
I am however BPA registered!

Posts about a tripping RCD and a garage supply stick in the mind.

(BPA = British Pyrotechnists Association)
 
Ive never yet bothered with the JIB, and I'm not sure I'd get a very good grade even if I did.
I am however BPA registered!

Posts about a tripping RCD and a garage supply stick in the mind.

(BPA = British Pyrotechnists Association)

Neither do i, when i did it was because i had to.

Rcd tripping, read the thread, i posted that before i went to the job as i had already been there previously and found a faulty appliance, i found the second fault within 20 minutes and i had previously mentioned it to the customer the first visit. Imo doesnt display any incompetency?

Garage supply, i dont think people quite got where i was coming from on that one and it was taken as i was asking for a step by step guide, which i wasnt, maybe i should of outlined my question abit better, i'll hold my hands up on that one. The reason i asked was to get an opinion as i said i just come off 6 months working in rewire teams on high-rise council flats and seeing nothing but trunking an T&E.

Didnt need to explain myself but i have. I got arsey because ive seen people get jumped on on here quite often and it sort of makes out that they know everything and quite frank they dont and it just comes as being arrogant and its not always necessary, i come here to give/take advice not to be jumped on over a mis-typed post about a price.
 
Neither do i, when i did it was because i had to.

Rcd tripping, read the thread, i posted that before i went to the job as i had already been there previously and found a faulty appliance, i found the second fault within 20 minutes and i had previously mentioned it to the customer the first visit. Imo doesnt display any incompetency?

Garage supply, i dont think people quite got where i was coming from on that one and it was taken as i was asking for a step by step guide, which i wasnt, maybe i should of outlined my question abit better, i'll hold my hands up on that one. The reason i asked was to get an opinion as i said i just come off 6 months working in rewire teams on high-rise council flats and seeing nothing but trunking an T&E.

Didnt need to explain myself but i have. I got arsey because ive seen people get jumped on on here quite often and it sort of makes out that they know everything and quite frank they dont and it just comes as being arrogant and its not always necessary, i come here to give/take advice not to be jumped on over a mis-typed post about a price.

I have read the threads, I have formed an opinion based on them and other posts, much as I am sure you have formed opinions on mine and everyone else's posts. I'm not going to pick them apart and criticise, nor argue about it.

Communicating in a written form on the forum gives the opportunity to proof read posts and edit them for a short time after posting. If after writing the posts, reading through it to check for errors, and then checking it again once posted, you have not managed to communicate effectively and in a precise and technical manner then you have only yourself to blame.
I appreciate that some people have difficulty with spelling or communicating through written English, but on a forum you have no time restriction on how long you spend writing a post so everyone should be able to have proof read and reviewed their posts before posting.
This is after all a technical trade based in both scientific theory and practical ability so everyone here must be capable of effective technical communication to be able to practice their trade so there is no reason not to write clear and understandable posts.
 
I have read the threads, I have formed an opinion based on them and other posts, much as I am sure you have formed opinions on mine and everyone else's posts. I'm not going to pick them apart and criticise, nor argue about it.

Communicating in a written form on the forum gives the opportunity to proof read posts and edit them for a short time after posting. If after writing the posts, reading through it to check for errors, and then checking it again once posted, you have not managed to communicate effectively and in a precise and technical manner then you have only yourself to blame.
I appreciate that some people have difficulty with spelling or communicating through written English, but on a forum you have no time restriction on how long you spend writing a post so everyone should be able to have proof read and reviewed their posts before posting.
This is after all a technical trade based in both scientific theory and practical ability so everyone here must be capable of effective technical communication to be able to practice their trade so there is no reason not to write clear and understandable posts.

:willy_nilly: Not really getting anywhere here are we. As im on my phone and this forum keeps reloading the browser halfway through messages, i type my posts and press done, thats it. Ive said that on numerous posts. Now im off to go listen to my new bon jovi album.

g'night matey
 

Reply to Full Certificate and Minor Works Certificates in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
889

Similar threads

Thank you all, yes I didn’t think they do and I have done minor works but the helpline was not very helpful. Got my yearly assessment soon so I...
Replies
4
Views
284
It applies to commercial if it shares the same supply as a dwelling.
Replies
4
Views
562

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top