wallyanker

Hi Guys

Just about to start a project on a new build. When i signed for all the paperwork on handover, it was described that the unit has a three phase 63a supply to an isolator, it is then our responsibility from there.

Get to the site this morning, the isolator is installed no problems but each phase has a 125a fuse. Is this normal as the fuse "upstream" is only 63a?

Thanks
Pete
 
not very discriminating is it, but still protected by 63 amp. might as well have links put in instead. Have you physically seen the 125 amp fuses or is that what the holder says on it?
 
Seen them this morning as I put a temp board in for the builders and dry liners. Just thought that they should be the same size or smaller than the 63a. Is there a reg against this or just bad practise?
 
Why has the supply got another set of fuses and not entering a DB isolator or is access to the primary fuses not available and if so this is not good.
 
Our unit is within a health centre and access to the supply 3 phase 63a is not accessible by us, unless we speak to the health centre manager to gain access to the main board. Our unit has something very similar to the below picture, 125a marked on each fuse inside the box.


[ElectriciansForums.net] Fuse ratings
 
What are you using the supply for? what load are you anticipating? could you replace the fuse links for lower rating ie40a or 50a even?
 
I have seen this type of thing before, where it is just used as a switch (Isolator, non fused), as one of the other posters has said, with copper links in place of the fuses.

If you think about discrimination, you would need to fuse down by half again, which would effectively reduce the current capacity of your supply significantly.

Nothing against the regs here as the supply is (or should be) already fused down to the requirement of the supply cable, and presumably you will be feeding a DB from this.
 
The unit will be fitted out to be a pharmacy, so not that heavily loaded. My point is, should the original installer have put in the same size, if not smaller fuses in the 3 phase box above to resolve discrimination? Is there any regs that state this? We have had all kinds of issues with the contractors who built this building, not fire painting steel supporting columns, etc, so need everything to be in order before we commence our fit out works.
 
My point is, should the original installer have put in the same size, if not smaller fuses in the 3 phase box above to resolve discrimination?

Why ?

Putting the same size fuses in it would not discriminate, and to put smaller ones in it they would need to be half of your 63 A OCPD feeding it.

Is this a final circuit ?, or is it just the Isolator ?, and is it going to be feeding a DB ?
 
It will feed a db that will then supply power and lighting circuits within the pharmacy unit.​


So no problem then, as your final circuits will be fused/OCP'd at the DB and provide some discrimination, it is a bit overkill, but ok nevertheless, as said it is just essentially an Isolator, and the fuses could be replaced with suitable copper links.​
 
Last edited:

Reply to Fuse ratings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
344
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
882
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K
  • Question
Why not fit a self contained SPD fed directly from the Henley blocks, and free up a bay? Could probably make one up from whats there, using a...
2 3 4
Replies
47
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top