I'm to install an extracter fan with a timer in a a brand new shower room. I got a question.
I also bought a 6A 3 pole fan isolator from Crabtree, it included instructions with diagrams on how to wire up a timed fan, to my dismay the diagram did not include a fused spur as it was coming from the light, is that allowed/right?? Just from the ceiling rose, to the isolator then to the fan.

The instructions from the fan says it needs a 3A fused spur and thought I agree. I've got into a bit of a muddle on how to wire up the fan which is operated when pull cord is pulled both the light and fan comes on, when switched off the light goes off but the fan remains running for a few more mins and thinking how do I include a 3 fused spur and drew a diagram below. (it includes 3 core +E and Tin and earth cables.
Please advise if wrong or unsuitable... http://imageshack.us/photo/my-images/32/fanwiring.png/
Many Thanks [ElectriciansForums.net] Fused spur fan
 
Last edited by a moderator:
that's really the only way, as you need bothe the L feeds, permanent and switched to the fan to be on a 3A FCU, so put the FCU before the light. 1 question, though. is the circuit RCD protected? it needs to be.
 
Are you sure thats only a 3 pole switch ??
There are 6A 4 pole switches on the market for isolating fans. I'm based in Ireland, but we use them all the time. Dont normally include a FSU, as they are only fused in one pole. Your wiring diagram is fine, but remember your only fusing the perm live, the switch live is unfused..
 
Are you sure thats only a 3 pole switch ??
There are 6A 4 pole switches on the market for isolating fans. I'm based in Ireland, but we use them all the time. Dont normally include a FSU, as they are only fused in one pole. Your wiring diagram is fine, but remember your only fusing the perm live, the switch live is unfused..

What do you isolate with the fourth pole? Earth? All a fan requires is L, SL, N and E so can't think what else you could switch. :confused:
 

Reply to Fused spur fan in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
351
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
313
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
367

Similar threads

  • Question
It can be easy to lose the sequence of things. If the fused spur has a neon indicator and this isn’t coming on then I wonder if -the original...
Replies
6
Views
846
Thank you. We do have a window. Do you think my idea (even if is adds complexity) is workable? Nothing fundamentally wrong that I am missing?
Replies
6
Views
708

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top