hello I've seen the page at the back of the regs book but nothing explains can you -
Have a spured socket off the ring using one cable and then put a fused spur after the spur and then feed additional sockets after the spir
I take it Wilson that you are referring to Appendix 14 of BS7671, the diagram shows all scenarios for a RFC and indeed the requirements for installing spurs from the RFC.
Your question would be a no you can't spur a socket using a single cable, and then add a fused spur to supply more sockets. What you could do however is swap the Spurred socket for a fused spur and then add as many sockets as you like, what you are suggesting amounts to 2 spurs from the same point. Hope this helps.
Upvote 0
Can you draw what you are asking. But it sounds like no, if I understand you correctly. Although saying that it hasn't stopped many others from doing so from what I see when attending various sites.
Aha manitas de plata has beat me to it.
Upvote 0
There is nothing to stop you having two spurs from the socket on the ring.
One spur to the additional socket, one spur to the FCU/
There is a physical problem of cramming 4 x 2.5 conductors into the back of the socket.
If I was you, I would do as Pete says above
Upvote 0
If I read correctly then no you can't do what you suggest. Think about the maximum potential load on the first section of cable spurred from the ring.
Upvote 0
TTC I think the OP was wanting to spur off of a socket to another socket using a single 2.5, and then from that spurred socket to another fused spur to feed some more sockets
Upvote 0
Reply to Fused spur off ring main regulations in the Electrician Courses : Electrical Quals area at ElectriciansForums.net
It can be easy to lose the sequence of things. If the fused spur has a neon indicator and this isn’t coming on then I wonder if -the original...
Luckily when I rejigged the socket to fit the fcu next to it, it meant the original ring wiring reached, i put the socket on the ring and took a...