Hello there,

I have my 1st assessment on monday and have a few questions about fused spurs throughout the house where i have changed the distribution board(nothing else).

1st I have a security light coming off the downstairs ring from the kitchen and i can't find any spur for that(and have no idea which socket it comes off), should i just note a deviation from the regs?

2nd i have a shaver socket in the downstairs toilet directly behind a light switch, does that need a fused spur? My thinking is there's not really any significant run of cable to protect?

3rd i have a shed (spurred off the kitchen ring) with 2 power sockets, and 1 lighting circuit that comes off a junction box(in shed) hence no fused spur for the lights although the cable supplying the lights is 2.5mm(same as socket), bearing in mind i thought fused spurs were primarily to protect the cable should i fit a 3 amp there or just note it as a deviation from the regs?

Thanks for reading.
 
Hi mate.
if you've only changed the board than providing all test results are satisfactory than that is where your reasponsibility lies, to make the system safe for use.
The points you have made di not make it unsafe just small areas of imorovement.
Take a mental note of them in case you are asked but dont worry.
With regards to the shed have you made sure this is up to scratch.
Ie earthing, cable current capacities. Loading of the circuit its spurred off?

Sent from my GT-I9100 using Tapatalk
 
Hi mate.
if you've only changed the board than providing all test results are satisfactory than that is where your reasponsibility lies, to make the system safe for use.
The points you have made di not make it unsafe just small areas of imorovement.
Take a mental note of them in case you are asked but dont worry.
With regards to the shed have you made sure this is up to scratch.
Ie earthing, cable current capacities. Loading of the circuit its spurred off?

Sent from my GT-I9100 using Tapatalk

Yes thankyou Simple Simon, the Zs's are ok in the shed except maybe the light which was slightly over what is required for a ring main, but it's a light so I'm hoping that's ok?
 
No wishing to teach you to suck eggs but you have checked/upgraded the bonding haven't you?

Re the shed light - is the neutral at the switch? If so you could change the standard light switch for a SFCU and fit a 3A fuse.
 
No wishing to teach you to suck eggs but you have checked/upgraded the bonding haven't you?

Re the shed light - is the neutral at the switch? If so you could change the standard light switch for a SFCU and fit a 3A fuse.

Thanks Murdoch, replacing the switch will work I think.

With regards to the main bonding I thought I had checked it all, although just realised the main bonding is only 10mm and the services only 6mm.
I have now added a 6mm earth to the MET to make 16mm, and also added a 6mm earth to the gas service pipe to make 12mm.
Unfortunately the water supply earth disappears to the back of the house where the cut off tap is so it will be hard to upgrade by tomorrow!
 
Thanks Murdoch, replacing the switch will work I think.

With regards to the main bonding I thought I had checked it all, although just realised the main bonding is only 10mm and the services only 6mm.
I have now added a 6mm earth to the MET to make 16mm, and also added a 6mm earth to the gas service pipe to make 12mm.
Unfortunately the water supply earth disappears to the back of the house where the cut off tap is so it will be hard to upgrade by tomorrow!

OOPS :goofy:
 
Thanks Murdoch, replacing the switch will work I think.

With regards to the main bonding I thought I had checked it all, although just realised the main bonding is only 10mm and the services only 6mm.
I have now added a 6mm earth to the MET to make 16mm, and also added a 6mm earth to the gas service pipe to make 12mm.
Unfortunately the water supply earth disappears to the back of the house where the cut off tap is so it will be hard to upgrade by tomorrow!

brush up on your earthing and bonding too as you dont seem to know which one is which
 
how is the shed fed from the ringmain? is it just spurred straight of a socket or is the a 13A fcu?
what cable is feeding the shed and how does it get to the shed ie clipped? buried? As has been said you are ony responsible for the CU change and the testing of all the circuits, any deviations from the regs should be noted
 
Last edited by a moderator:
how is the shed fed from the ringmain? is it just spurred straight of a socket or is the a 13A fcu?
what cable is feeding the shed and how does it get to the shed ie clipped? buried? As has been said you are ony responsible for the CU change and the testing of all the circuits, any deviations from the regs should be noted

shed is spurred of a 13A fcu, swa is 4mm live conductors and 2.5mm cpc, buried cable. The junction box in the shed looks as if it would fail it's IP rating as I could easily stick a finger in there.
 

Reply to Fused spurs in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
It can be easy to lose the sequence of things. If the fused spur has a neon indicator and this isn’t coming on then I wonder if -the original...
Replies
6
Views
929
K
  • Question
Ah, I see. The op question is ambiguous, and I took it that he wanted to add a socket for a washing machine from and exiting switch fused spur. A...
Replies
10
Views
885

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top