P

Piratepete

Hi Guys.
Just done a rewire which includes a 32 Amp 6mm cooker supply to a cooker outlet point via the usual isolator + socket.

This is only being used for an oven which turns out to be 2.7 Kw, with an HR 1.5mm flex requiring a 13 Amp fuse.

Would it be acceptable to change the outlet point to an FCU (which will be hidden behind the oven)? Guess that's no worse than having a hidden plug and socket! Not quite sure whether 6mm cores will fit in a FCU, but I'm always willing to try!
Cheers.
Pete
 
THE PROBLEM IS THAT OLS CHESTNUT " MANUFACTURERS INSTRUCTIONS". IF YOU DON'T FUSE IT DOWN TO 13a, THEY CAN DISCLAIM RESPONSIBILITY IF AND WHEN IT GOES WRONG.

They can always try, it'll hold no water.... As i said the BS 1362 fuse is to protect the cable/cord of the appliance, NOT the appliance/equipment itself!! Could always ask them what they would recommend for the same unit being installed in say France or Germany!!! That'll be an interesting answer to hear, if the same question is asked in a court of law?? lol!!
 
totally agree. it's same as the 3A fuse in bathroom fan. the problem arises in court " you did not install it to manufacturers instructions" even if said instructions are stupid.
 
totally agree. it's same as the 3A fuse in bathroom fan. the problem arises in court " you did not install it to manufacturers instructions" even if said instructions are stupid.


Ask them the same question, ....What is the manufacturers instructions given to those installations where this same bathroom fan is installed in Europe?? Can't come up with a 3A fuse can they??!!!!! lol!!
 
Never known a case to go that far. It's normally the manufacturers service agents that try all this smart arse stuff out, with the chopping of moulded plugs and the like.... If an appliance has been connected to the electrical supply by a qualified electrician, in a manner that fully complies to BS 7671, then the manufactures ''will'' back down, as they have absolutly nowhere to go.
Apart from the fact that it wouldn't be in the companies brand names best interests on several counts, to allow such cases to even come close to a court hearing ...

Down to you, if you are willing to let a service agent deny you and/or your customers consumers Statutory Rights!! Buggered if i ever would!!
 
I agree with you I don't doubt it for a second, but arguing with the service agent how evert get may be doesn't get the cooker / hob fixed in the short term, the customer won't care who's fault it is they just want to cook! Even if the manuf did back down eventually I still can't see a customer being over joyed. I've wired up some beasts of cookers and hobs and the cost of them was frightening, I would adhere to manuf instructions as Long as they were inline with 7671 as coving the cost of the item even in the short term or to have the possibility of that hanging over me was not a option. If that meant waiting a day or so for some 6 or 10mm H07 then so be it, if your self employed there enough to loose sleep over without adding to it!

Hats off off to those who have the time and energy to fight their corner, but that wasn't for me.
 

Reply to Fusing down the oven. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Since my last post I have used the oven several times and it is still working ! On reading the 'regulatory' position I will ask an electrician to...
Replies
9
Views
2K
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top