Fusing downstream with very short cable length | on ElectriciansForums

Discuss Fusing downstream with very short cable length in the UK Electrical Forum area at ElectriciansForums.net

Joined
Aug 26, 2022
Messages
8
Reaction score
6
Location
Cambridge, UK
Hi, first post newbie here.

I have a question relating to what I am told is a grey area in both 7671 and low voltage assemblies regs. I have a customer with some LV industrial control panels, 100A fused isolator with 25mm main singles from isolator down to motor drive, but off the isolator terminals are also some short 6mm cables that go immediately to 1A fuses (within 3 or 4 inches). I am aware obviously this contradicts the requirement for conductor CSA rating to be > upstream protective device rating, but also on the other hand have been told in the past this is fine to do as long as the under-rated cable is of sufficiently short length, there is no danger of mechanical damage to the cable, and the design load of its downstream circuit is suitably low - I believe all of those to be true in this case. So the opposite of de-rating I guess! Has anyone had a similar quandary in the past, and if so were able to find a definitive answer within the UK regs?

Entire circuit is enclosed within a steel control panel. Drawing attached, as well as layout sketch of the installation, unfortunately I don't have photos of the actual installation sorry.

Thanks in advance
Ed

[ElectriciansForums.net] Fusing downstream with very short cable length


[ElectriciansForums.net] Fusing downstream with very short cable length
 
See 433.2.2 and 433.3.1 especially ii)

Main alarm bell - is the neutral fused?
The circuit diagram says not, the text and other picture says so.
 
This sort of thing is done all the time for voltage inputs of sub meters etc. The main problem I've seen is undersized breaking capacity of the fuses.
 
Most panels at my current workplace run some alarmingly small cable off the incomer to door indicators, fuses add a point for possible confusion around the status of the panel it's argued. Admittedly these are designed to 60204-1 rather than 7671, but they're largely similar on matters such as this.
It has, and seemingly always will be a hot topic. The means of termination is also worthy of note, a very large and very small cable wedged in one terminal is not ideal.
 
See 433.2.2 and 433.3.1 especially ii)

Main alarm bell - is the neutral fused?
The circuit diagram says not, the text and other picture says so.
Thanks Tim, yes the neutral is fused now, there was a fuse carrier with a solid link when we first looked at the panels but have advised the customer to drop fuses in instead - hence why the drawing shows no fuse on the N side.
 
Thanks Tim, yes the neutral is fused now, there was a fuse carrier with a solid link when we first looked at the panels but have advised the customer to drop fuses in instead - hence why the drawing shows no fuse on the N side.
That was bad advise they make neutral links for a reason.
 
Last edited:
That was bad advise they make neutral links for a reason.
My mistake, I'm being told this was another circuit that took 400v off 2 phases to feed a 400-110v transformer, this is where a solid link was found in one of the fuse carriers and advised customer to replace with fuse as is a live phase, the neutral link was left in on the single phase circuit pictured down to the heater. Corrected the below
 

Attachments

  • [ElectriciansForums.net] Fusing downstream with very short cable length
    downstream fusing 2.jpg
    232.8 KB · Views: 30
Excellent, the 1.5 cable is its own fuse :laughing:
I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over damaging everything before taking out the ACB. The conductor on the other side of the bolt is a 240mm2 Cu-Flex.
 

Reply to Fusing downstream with very short cable length in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
673
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
573
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
392

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top