If we have 3 x 2500wp single string arrays on a 3 phase supply (split evenly over phases) using SMA 2500HF's will we need a G59 relay for sure or is it up to DNO? The SMA's are not G59 as far as I know only G83.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss G59 Relay in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
To ENA for a G83/1 Stage 1 Application
f) can you confirm the maximum Watts applicable to a 3-phase supply?
Answer:
f) 230x3x16= 11,040 for practicable purposes this is 11kW, split evenly over three phases. The following is not allowed
phase 1 4kW
phase 2 4kW
phase 3 3kW
as two phases exceed 16A per phase
Unbalance is allowable up to to the following limit
phase 1 3.7kW
phase 2 3.7kW
phase 3 any value under 3.7kW