I received a reply this afternoon from the Energy Network Association to the questions raised about various G83 issues. Their reply is reproduced below with the original questions added back in
in bold to aid readability. (I've not corrected any of the minor typos in the reply.)
Date: Tue, 22 Feb 2011 18:02:52 +0000
From: David Spillett <
[email protected]>
Please find my response to your questions below.
Firstly In relation to the reference of refusal to connect above 1.9kW, G83/1-1 2008 caters for Small Scale Embedded Generators upto 16A per phase (3.7kW single phase and 11kW 3 phase). I am not aware of any DNO refusing connections above 1.9kW unless possibly there may be safety related concerns or equipment is not type tested as required by G83/1-1. G59/2 (2010) caters for connections above 16A per phase.
Q1 - DNOs are allowed to use their discretion to accept a >16A per phase system under G83 terms, based on their knowledge of the local network capacity. Once a DNO gives their agreement on this basis is this decision irrevocable or are they allowed to change the terms at a later date (when other changes may have happened in the meantime, such as additional G83 systems being connected in a locality) and then request that the original system complies with G59 - including requiring the customer to pay any associated DNO costs? Also clarify this matter where such multiple systems (such as wind and PV) may be connected at a single location over a period of time where, taken individually, each system comes below the G83 threshold but, taken together, they may exceed it.
DNOs were... and still are.. but the protection settings should conform to G59/2. Contracts can always be renegotiated - and if a customer doesn't like this, they can go to Ofgem for a determination.
However this is the formal background and I would not expect a DNO to change any terms retrospectively for domestic scale customers.
Where G83 applications in the same locality are genuinely independent, they would be treated as such and no reinforcement costs charged to any of the applicants. However, if "multiple systems...connected at the same location" means all within the same premises, it should be expect that DNOs will aggregate the electrical output of those individual sources of energy, in deciding whether or not the 16A per phase limit had been reached.
If multiple systems, each less than 16A are connected at different connection points but in the same locality then stage 2 of G83 is applied.
Q2 As regards multiple G83 connections, in a single locality at the same time, are the costs of any required network reinforcement, that may be required to accommodate these, to be passed on to customers or to be borne by the DNO?
The cost of any works to facilitate the connection/s will be assessed in accordance with the DNOs “Statement of Methodology and Charges for Connection to the distribution system.
Q3 Can we get clarity as to exactly what the 16A per phase limit for G83 actually relates to? Is it based on:
a) the Declared Net Capacity or the Total Installed Capacity of the system (as given on the MCS commissioning certificate) ?
b) the manufacturers quoted peak output of the PV panels (or other applicable prime mover 'nameplate' figure) ?
c) the maximum grid-tie inverter output?
d) if it is based on the inverter output then is it based on the manufacturer's maximum rating for the model of inverter or based on the (sometimes programmable) actual maximum inverter output figure
e) figures used at a - d above are usually given in Watts - so, in order to convert to Amps, is 230V or 240V to be assumed? I believe the definition in G83 specifically states "230V ac" but many DNOs seem unaware of this minor fact.
f) can you confirm the maximum Watts applicable to a 3-phase supply?
(a) For Inverter systems it is the output of the inverter so it would be possible to install a 3.6kW inverter with 4kW peak of PV panels under G83
(b) No see answer above
(c) Yes see answer above
(d) maximum continues rating
(e) 230 volts is the nominal voltage for the whole of Europe
(f) 230x3x16= 11,040 for practicable purposes this is 11kW, split evenly over three phases. The following is not allowed
phase 1 4kW
phase 2 4kW
phase 3 3kW
as two phases exceed 16A per phase
Unbalance is allowable up to to the following limit
phase 1 3.7kW
phase 2 3.7kW
phase 3 any value under 3.7kW
Q4 Question directed to Ofgem
Q5 How might the G83 threshold apply in a situation where a >16A per phase system has been designed to prevent no more than 16A per phase from being exported; e.g. a controller and dump load used for on-site heating for any excess that might be generated?
The system would need to be type tested for G83 to be applied.
Best Regards
David Spillett
Energy Networks Assocation