G99 GSI-3 4.4 kw Victron inverter install with EES and batteries and installer can set the export lint if required by dno
As part G99 GSI-3 you required carry out phase to neutral loop impedance and phase to earth loop impedance test not a problem. but the must be 180 m ohms or less for phase to neutral loop impedance on site from consumer unit with it switch off and earth connection removed temporarily to remove metallic parallel paths and reading back to the dno transformer secondary side
and a phase to neutral loop impedance 180 m ohms or less but the reading form site are 0.309 ohms on TN-S 60 amp supply but as cut fuse holder is not marked with the fuse rating i.e. 60/80 or 100 amp as you fond in new install is (one being 1950) and only based on 16mm2 meter tall 87amp prox
has anyone had the same problem or is a case of me misinterpreting SSE G99 GSI-3 information in the web site
As part G99 GSI-3 you required carry out phase to neutral loop impedance and phase to earth loop impedance test not a problem. but the must be 180 m ohms or less for phase to neutral loop impedance on site from consumer unit with it switch off and earth connection removed temporarily to remove metallic parallel paths and reading back to the dno transformer secondary side