oldtimer

Hi guys
Did some work in a house where there is a 12 way DB TNS and a 30A switched fuse for a garage / workshop (2 levels) about 30 metres from the house.Both DB and 30A SW/fuse are connected to live blocks from the meter.

The garage is supplied via a 6mm LNE run in galvy conduit supplying a 4 way wylex board and the Zs is 0.66 an PFC is 0.54 L-N and 0.35 L-E .

The customer wants a quote to upgrade the DB so here is my thoughts and would appreciate any feedback.

Install a 15 twin RCD board each RCD has 6 breakers so thats the house covered and the DB has 3 unprotected ways. My thought was to change the DB and in the future fit a 32A RCBO into the non protected side of the board for the garage supply replacing the 30A SW/fuse with a 45A switch and replaceing the old 4 way rewireable fuse board in the garage with a 4 way circuit breaker board.
The board has 2 x 5A and 2 x 16A fuses ie power and light for each level.

Also to point out the build looks like a 2 double garages one on top of the other.

Socan I do this and what is the definition of this Garage/workshop

Many thanks

Just to ad the DB Zs is 0.15 , PF 2.4 L-N , 1.5 L-E
 
Last edited by a moderator:
sounds fine to me providing calcs are all in order and vd is ok, although i would fit a small cu with rcd in the workshop to save walking to house if rcd trips, the supply cable is mechanically protected.
 
Thanks for the reply the reason why I thought about fitting the RCBO at the CU in the house was that it covers the supply cable throughout the house in in the conduit running along the garden wall.

As for VD I measured 235 at the board and 233 at the garage.

The reason I was looking for clarification was I have never had this situation before plus I remember reading here about detached garages and earthing
 
Hi oldtimer. if .as seems likely , there is extraneous conductive parts in the Garage / workshop then you will have to either
1. Run in a 10mm Main Bonding conductor from the Met to these E.C Parts...or
2. Convert the exterior supply to TT. inc a rod installation.
 

Reply to Garage can I do this in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
625
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
955

Similar threads

Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
322
  • Question
wouldn't surprise me if we adopt this sooner or later...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top