ceejay
Is it necessary to install a garage consumer unit with an rcd if the feed is coming from an rcd protected main board? i don't think it is but want to make sure. It will be running a small ring and a lighting circuit.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss garage consumer unit in the UK Electrical Forum area at ElectriciansForums.net
Hi guys I have a similar question so thought I'd jump in on this thread.
I've been asked to install a six way fuse board in a garage. The new fuse board will be used for a combi boiler supply (boiler situated in garage), garage power and lighting and a 32 amp jacuzzi in the garden.
The house fuse board is being renewed and will be upgraded to a split load 100a rcd board. The supply is TNS
Like the above suggestion I was planning on splitting the supply tails via a henley block, feeding both the new rcd fuse board and some kind of double pole switch in an enclosure. From that double pole switch I was going to run a 10mm 3 core swa into a new rcd garage board.
Does this sound OK?
Many thanks.
In that case would placing a double pole MCB in the enclosue be the answer (rather than a double pole switch)
what rating MCB would be recommended?
Hmm, double pole MCB. Why would you want to do it like that? They are used a lot in petrol stations and sur le continent but around here the usual way is to use a switch fuse. One of these, eg
Click DB750 80a Switchfuse
I'm a bit worried about your next query
I've got a feeling that you don't understand what the switchfuse would be for. You should not be doing this if you don't know what a fuse protects.
I've been an industrial electrician for the last 11 years. I'm just not too familiar with this house bashing malarke and what the standard is. .
No, I'll down size the fuse rating. Any advise on fuse sizing anyone?
I changed the consumer unit today. I have three spare ways in the split load board and a bit of bus bar left over. My new way of thinking is that I can a run a 10mm t and e with a 10mm earth from the non rcd protected side of the board backed up on a 60 mcb. .
This seems like a lot less work for me and will be a lot less expensive for my customer
For what its worth, I'd use a metal CU for better protection, and mount the board a little higher up the wall than I would in a house.
Sector/Senate do a 2 way metal cu with 63A main switch for ÂŁ28.80 + VAT so that's hardly expensive, especially as its quicker to install 1 item, than terminate the SWA into a metal enclosure etc, etc.
Also I'd like to add that as far as I'm concerned there is nothing wrong with someone else signing of an installation if they have fully inspected it and are satisfied that it complies with bs7671 so it is far form a lie.