Recently did a house rewire and am about to start the garage next to it. I have a 10mm armour feed from a 40a RCBO in the house. The garage is a double with a room upstairs and has an outbuilding attached. So im gonna have 2 rings, 2 lights, elec door, compressor. Am i ok to get a dual RCD board for the garage.??I dont see why this would b a problem but a small gagare cu simply wont do the job.Cheers
 
Couldnt get the swa directly into board because suppliers feed cable dropped down into wall and into outside box and then from meter back into wall again so i steered clear. Got an adaptable box next to CU. so made swa off into adaptable box on outside, through wall in conduit into another adap box. As swa doesnt go directly into board am i advised to keep RCBO.Cheers ROBO
 