W

william7900

Hi friends,

I have been reading threads concerning garage earthing arrangements. Advice was given to extend the earth from the house to the garage. Please may I comment that this is a dangerous practice because if by accident someone went through the SWA cable with the mower etc, the result would be catastrophic, due to the fact that in the garden you will be in contact with the earth and a perfect conductor for electricity and receive a severe shock. The earthing system for a garage should always be TT, using earth rods and trying to achieve a resistance of 200 ohms. You may have to use more that 1 earth rod to acheive this. The garage unit should always be RCD protected.

This is why on building sites all the equipment is supplied by transformers which gives a separated environment and no earth is used for safety. Hope this helps.

Regards,

Bill
 
It's unreal that there are these people, still around out there!! These people will happily go around making TT systems willy nilly, probably using those 3/8'' 1.2 m excuse of ground rods, that can very easily leave an installation void of any earthing during adverse weather/temperature conditions. Because they know no different, they will ditch a superior earthing system and will spurt out this total nonsense about ''it is forbidden'' to export PME!! who the hell told you that?? Well....how about ''Extending the equipotential zone then?? I take it, you then think that an outside socket outlet on a PME system is also banned??


William, the only confusion in what you have posted is yours, as you obviously have no idea what your saying here. You have been wrong in just about everything you have posted on this subject. Please go and read the Sticky on this subject, then come back here and try and tell us that were all wrong and that your right!!
 
Guys,

The suppliers do not reccommend it as a matter of safety. This is why we have regulations to protect us in that 1 in a million chance of being injured. Unfortunately not all of us wish to adhere to them until it affects us. Just as a matter of interest the part P of the building regulations came about due an MPs daughter being injured by an electrical fault.

Keep safe guys.

Regards,

Bill
 
Bill that last reply is vague and unhelpful to your pointless arguement. Firstly you said the DNO does not allowed us to export a PME earth now you say they don't recommend it. Which is it? Which reg are you talking about. There have been a few others that have said about regs but could not find this hidden reg to back up their argument. You are wrong plain and simple. Just give up with argument.
 
Take a look at this Bill.
http://electrical.------.org/wiring-matters/16/elect-inst-outdoors.cfm?type=pdf


Sorry for the repetition - Just spotted someone further back has already pointed this document out.
 
Last edited by a moderator:
Guys,

Just as a matter of interest the part P of the building regulations came about due an MPs daughter being injured by an electrical fault.

Keep safe guys.

Regards,

Bill
She wasn't injured, she was killed. However, her death came a long time after the consultation process began which resulted in Part P. Merely a tragic coincidence.
 
Guys,

The suppliers do not reccommend it as a matter of safety. This is why we have regulations to protect us in that 1 in a million chance of being injured. Unfortunately not all of us wish to adhere to them until it affects us. Just as a matter of interest the part P of the building regulations came about due an MPs daughter being injured by an electrical fault.

Keep safe guys.

Regards,

Bill


Stop, and think about what your saying. Based on your electrical knowledge on how earthing/bonding systems work you will come to the same conclusion as the vast majority here. Your basing your reasoning at the moment, on myths and scaremongery that originated from those that opposed the introduction of PME in any form for general distribution.

As i stated in earlier posts, you have been wrong in just about everything you have posted on this subject to date. You are also very wrong in the ''one in a million'' statement, the chances of experiencing let alone being injured, is far far greater than that!!

The only restrictions to the use of a PME system are well founded, but do NOT include extending such a system to a domestic outbuilding, shed, or garage!!
 

Reply to Garage Earthing system in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
328
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top