Hi,

i went ent to look at a job this morning where someone needs power to a remote garage in the garden, it's only about 8 - 10 meters away from back of house.

unfortunately it's not really feasible to run it on its own circuit for quite a few reasons, yet this would have been my preferred method.

is the general accepted method when coming off a ring to essentially create a lollipop circuit, so connect from ring to SWA back to small garage cy, is the accepted method just put a 13A FCU off the ring and run a bit of 2.5 swa to a garage cu?

obviously I'll check the zs and R1+R2 at point of spurring to calculate max length of spur.

is this what you would do if cannot get it on its own circuit? Or would you just spur off with 4mm and take that direct to a garage cy without the 13a FCU?
 
Hi,

i went ent to look at a job this morning where someone needs power to a remote garage in the garden, it's only about 8 - 10 meters away from back of house.

unfortunately it's not really feasible to run it on its own circuit for quite a few reasons, yet this would have been my preferred method.

is the general accepted method when coming off a ring to essentially create a lollipop circuit, so connect from ring to SWA back to small garage cy, is the accepted method just put a 13A FCU off the ring and run a bit of 2.5 swa to a garage cu?

obviously I'll check the zs and R1+R2 at point of spurring to calculate max length of spur.

is this what you would do if cannot get it on its own circuit? Or would you just spur off with 4mm and take that direct to a garage cy without the 13a FCU?
You are an apprenticed sparks aren't you?????
 
No it's not ideal, I certainly wouldn't do that. This one would be s right pain to get s new circuit in maky due to the route the cable would take, and there is a cost issue as I know that option is going to be too expensive, but to run it off the back wall through a fcu would work well, I guess if it was switched it could be used as s point of isolation for the garage. They only want to plug s sodding tumble dryer in, I think I'd be more enclined to find space in the house for it.
 
no problem with 2.5 swa, providing loop is good ie. ze +r1+r2. and the ring circuit has rcd protection. only issue would be pain in the butt tripping of the rcd if the garage is liable to damp and moisture. [nuisance tripping] and you are protecting the spur with a fso.
 
Last edited by a moderator:
Hi,

i went ent to look at a job this morning where someone needs power to a remote garage in the garden, it's only about 8 - 10 meters away from back of house.

unfortunately it's not really feasible to run it on its own circuit for quite a few reasons, yet this would have been my preferred method.

is the general accepted method when coming off a ring to essentially create a lollipop circuit, so connect from ring to SWA back to small garage cy, is the accepted method just put a 13A FCU off the ring and run a bit of 2.5 swa to a garage cu?

obviously I'll check the zs and R1+R2 at point of spurring to calculate max length of spur.

is this what you would do if cannot get it on its own circuit? Or would you just spur off with 4mm and take that direct to a garage cy without the 13a FCU?


As Murdoch said, do what is safe. It is entirely up to you, you are the artificer of this, no one else.


I would at the very least have it through a double pole fused spur but far from ideal, but often things are.
 
why not? there is nothing bad about taking a fused spur from a ring main if the other option is too difficult. before you run the spur, measure the phase and earth resistance of the swa [easy done if you know the length of run, the phase will be the same as the earth in swa] you can check the values in the ie regs also. then add to the loop impedance of the ring main, which will include Ze, and bobs your uncle if your values are within the limits given in the ie regs. as you know when you plug in your loop impedance meter it calculates the entire loop back to the supply traffo.
 
Last edited by a moderator:
why not? there is nothing bad about taking a fused spur from a ring main if the other option is too difficult. before you run the spur, measure the phase and earth resistance of the swa [easy done if you know the length of run, the phase will be the same as the earth in swa] you can check the values in the ie regs also. then add to the loop impedance of the ring main, which will include Ze, and bobs your uncle if your values are within the limits given in the ie regs. as you know when you plug in your loop impedance meter it calculates the entire loop back to the supply traffo.

I'll do him a quote based on this route and if he accepts I'll pop round and take a couple of measurements.

Like i say I usually just fuse it down and run it from there, it's a shame I can't run it all the way back to the CU, unfortunately thete are too many obstacles and obstructions let alone a Tarmac driveway and steps up to the front of the house in the way.
 
So you're going to quote on the basis of a wet finger in the air and then take some measurements?
Good grief! Quote on the basis of what you know, do it properly because that way nothing can come back and bite you on the arse.
Quotes are binding, estimates are not.
 

Reply to Garage supply in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
315
I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
462

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top