Hi,

I just recently bought a house and the garage has a supply coming from the house CU via a 40amp MCB which runs into a IP66 rated 13 amp double socket in the garage, I'm almost certain the cable size is 4mm (SWA cable).

Ive just recently finished an electrical engineering apprentership and im just after some more experienced advice about this.
I want to install a new roller shutter door some led lighting along with maybe a few sockets.

I planned on removing in 13amp socket an adding another CU in the garage with a 40Amp 30mA RCD, 32amp MCB (for sockets) 6amp breaker (lighting).

Any advice on this would be more than greatful.
 
16 or 20 amp would normally be more than ample for a garage sockets. Most garage DBs come with 16 and 6 amp MCBs as standard.

Handy having a 40 amp supply to the garage though as this leaves options in the future for upgrades such as electric vehicle charging point.
 
what do you plan on running in the garage? 32 amps seems a bit excessive for occassional use out there?
Literally nothing the odd power tool, maybe a jet wash at the most and a lighting circuit
what do you plan on running in the garage? 32 amps seems a bit excessive for occassional use out there?

Not a great deal really, a garage roller door, occasionally a few poor tools and a lighting circuit (LEDs). Would you recommend putting in a smaller CU in the garage in this case then?
[automerge]1580577102[/automerge]
16 or 20 amp would normally be more than ample for a garage sockets. Most garage DBs come with 16 and 6 amp MCBs as standard.

Handy having a 40 amp supply to the garage though as this leaves options in the future for upgrades such as electric vehicle charging point.
In this case would you advise putting in a smaller Main CU at the garage end?

At the most it will be running at any given time is a roller shutter door with some LED lighting.
 
fit a standard garage board on the end of the 4mm ( it may be 6mm if on a 40A MCB). RCD and 1 x 20A (or 16A ) MCB and 1 x 6A MCB.
 

Reply to Garage supply in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
426
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
543
Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
339

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top