regarding a new supply to a garage. can someone point me in the direction of the regs book or on site guide where it says the rcd protection should be located? In the garage cu itself or a seperate rcbo in the property cu. . .. . . may seem a daft question but need some clarification.

thx in advance

hahahah. . .. just seen a post all about garage suplies and the location of RCDs.

So I recokon the answer to my question is. . . . if I have swa supplying the garage (which I will have)then the swa doesnt need to have rcd protection, because it is mechanically protected, and the rcd can go in the garage, as long as the circuit is on the non-rcd protect side of my consumer unit in the main properrty.

:D

. . . . just to add the cu is a 16th style split with one side rcd protected, and the other side non-rcd protected.
 
Last edited:
I took my inspector to a board that I had changed, the circuit to the garage was proteted through one of the two RCD's in the board, the CU in the garage contained a main switch only and two breakers.

He thought that was fine.
 
I took my inspector to a board that I had changed, the circuit to the garage was proteted through one of the two RCD's in the board, the CU in the garage contained a main switch only and two breakers.

He thought that was fine.

mmmmm, that is interesting! Iam assuming the CU was a 17th edition dual RCD?
 
If the garage is detached then would not the swa have to be rcd protected.

I would have thought the best place is at the original CU, either on the rcd side if 16th or with its own rcbo.
 

Reply to garage supply in the Australia area at ElectriciansForums.net

Similar Threads

  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K
  • Question
You need a CT clamp at main tails, it depends on the rules where you are - you used to be allowed wireliss ones (such as MyEnergi Harvi), these...
Replies
14
Views
3K
  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
642
  • Question
Yes that’s exactly right, thanks for your reply, it’s been very helpful
Replies
19
Views
3K
  • Question
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks