I have a 40amp typeB MCB (RCD protected) supply to an IP66 junction box in my garden which the runs in 4mm swa cable under my garden to the garage into a 13amp socket.

I want to fit a new consumer unit I'm my garage to run a lighting / ring main socket circuit. Question is can I just use the 32amp/6mp MCB supplied for this and do away with the 40amp 30mA RCD as it's RCD protected from the supply consumer unit in the house?
 
does the cable to the IP66 box require RCD protection?if not, change the RCD to a MCB (40A is wrong, you need max. 32A) and use the RCD in the garage board.in the garage don'tinstall a ring, install a radial with a 20A or 16A MCB.
 
The existing supply to the IP66 junction box is a 40amp MCB supply, which has seperate RCD protection along with all other circuits on the main CU. Reason for leaving it as a 40amp supply and not changing it to 32amp is the RCD in the garage is 40amp? Surely having a garage 40amp RCD (Main) off a 32amp MCB supply is wrong? It will have the potential to draw more than the designated Supply MCB?

Also any reason why you recommend a radial over Ring?
[automerge]1580757962[/automerge]
What is your earthing system.
TT earth system..
 
The existing supply to the IP66 junction box is a 40amp MCB supply, which has seperate RCD protection along with all other circuits on the main CU. Reason for leaving it as a 40amp supply and not changing it to 32amp is the RCD in the garage is 40amp? Surely having a garage 40amp RCD (Main) off a 32amp MCB supply is wrong? It will have the potential to draw more than the designated Supply MCB?

Also any reason why you recommend a radial over Ring?
[automerge]1580757962[/automerge]

TT earth system..
the RCD in the garage is therefore redundant. you need to replace with a 2 pole main switch like the one in the house CU. it's current rating (A) does not matter as long as it's over 32A. it's not a protective device. a 100A one will do just as well. it's just the max. current it's rated for.
 
You need a two way consumer unit with a non-rcd main switch, two mcbs at 20A and 6A. The existing 40A needs reducing to 32A. You won't achieve selectivity between devices but that isn't the end of the world.
Oh yes this also needs notification to building control.
 
A ring in a garage is generally over engineering things, a radial on a 16/20 is usually more than adequate for perhaps a freezer and a few power tools.
Personally I wouldnt bother with a CU, change the MCB at source to a 32a, extend the supply in the garage to however many sockets you want in 4.0mm, and use an FCU to feed the lights. You are then simply altering an existing radial, not installing a CU, no BC notification required.
 
You need a two way consumer unit with a non-rcd main switch, two mcbs at 20A and 6A. The existing 40A needs reducing to 32A. You won't achieve selectivity between devices but that isn't the end of the world.
Oh yes this also needs notification to building control.
When you say selectivity between devices can you explain more please?

Yes of course.
 

Reply to Garage in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
426
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
790
He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
637

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top