I bought a garbage disposal and had it installed under the sink by a plumber. When we attach it to the power, if the switch is turned on the disposal runs. When the switch is turned off, it trips the circuit breaker. I tried attaching a different switch, but it still has the problem. The clothes washer is plugged into this same circuit and works fine.
 
If it its a GFCI (or RCD) that is tripping, but is holding when the switch is closed, then there is no imbalance in the circuit. If a double pole switch is fitted, and one pole is opening very slightly before the other then a imbalance will be detected and the device will trip.

But until the op comes back and confirms what's involved then we can only speculate.
 
If it its a GFCI (or RCD) that is tripping, but is holding when the switch is closed, then there is no imbalance in the circuit. If a double pole switch is fitted, and one pole is opening very slightly before the other then a imbalance will be detected and the device will trip.

But until the op comes back and confirms what's involved then we can only speculate.
@Devon he stated it was on the same circuit as the refrigerator. That branch circuit is required to be installed as a dedicated circuit by the NEC and no GFCI is required. Having said that the plumber has tapped off that circuit which is not allowed. VIOLATION
 
If it its a GFCI (or RCD) that is tripping, but is holding when the switch is closed, then there is no imbalance in the circuit. If a double pole switch is fitted, and one pole is opening very slightly before the other then a imbalance will be detected and the device will trip.

But until the op comes back and confirms what's involved then we can only speculate.

I think the OP confirmed that it's the 30A MCB that's tripping.
 

Reply to Garbage disposal wiring problem in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Sorry for the late reply but if you don’t have it working garbage disposals are supposed to have their own circuit but I don’t know how old your...
Replies
1
Views
1K
Also posted in DIY. strange one in my kitchen. 3 sets of 2-way switched mains GU10 Philips down lighters. ( no dimmers) Have been fine for...
Replies
0
Views
173

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top