Hi all I was at a job and an electrician was fitting 2 patio heaters.
They were fed by a 4mm armoured and were 2Kw each which was fine.
He was doing a nice neat job but I did notice that he cut the plugs off the heaters and terminated the flex straight into the adaptable box via a stuffing gland.
I asked about them now not being fused at 13A but he said they are going on a 20A mcb and each heater is only drawing a maximum of just over 8.5A which is ok?
Is it? or should there be either a socket for them to plug into or a fused connection unit?
I didn't question further as he was an older chap and seemed to have been doing his job longer than I've been around.
Your views/opinions on this would be appreciated thanks.