Hello everyone,
I'm new in the industry, and soon will get 2 Level in Electrical installations.
At a class tutor gave us a homework, to make a diagram, and all necessary calculations for cable size, voltdrop, Zs, e.t.c What's needed in "real world".
I have a few questions about a schematic(?) wiring diagram, and in general. Pics are below.
For example, customer asked for 5 separate circuits(each of them will turn on individually), and 1 switch to turn all 5 circuits at the same time.
Length - 84m of wires required
Circuit 0 – all at the same time - 2140W / 230V
Circuit 1, 2 flood lights, 250W x2
Circuit 2, 2 beds 4 garden lamps, 120W x4
Circuit 3, 2 flood lights, 250W x2
Circuit 4, 4 tree lamps, 4 x 120W
Circuit 5, 4 brick lights, 4 x 40W
Questions are:
1) Is it possible to wire in that way, like in the pic2?
2) Which circuits are final here if a customer will turn on Circuit 0?
3) Customer can turn on circuits randomly e.g. 1-5, 1-2-3, 2-5-0. Then all circuits should be counted as final, and therefore 1.8 diversity factor should be applied to counting?
In that case:
Maximum demand = (2140W/230V*1.8(A1(Note 2)) * 0.66(A2) = 11.05A
Voltdrop (Reference method A)= (7.3*11)/1000*84=6.77V
Therefore, 6mm2 cable should be used. But it's quite costly, isn't it?
View attachment 25128View attachment 25129
wires will be buried in the ground.
Thank you.
I'm new in the industry, and soon will get 2 Level in Electrical installations.
At a class tutor gave us a homework, to make a diagram, and all necessary calculations for cable size, voltdrop, Zs, e.t.c What's needed in "real world".
I have a few questions about a schematic(?) wiring diagram, and in general. Pics are below.
For example, customer asked for 5 separate circuits(each of them will turn on individually), and 1 switch to turn all 5 circuits at the same time.
Length - 84m of wires required
Circuit 0 – all at the same time - 2140W / 230V
Circuit 1, 2 flood lights, 250W x2
Circuit 2, 2 beds 4 garden lamps, 120W x4
Circuit 3, 2 flood lights, 250W x2
Circuit 4, 4 tree lamps, 4 x 120W
Circuit 5, 4 brick lights, 4 x 40W
Questions are:
1) Is it possible to wire in that way, like in the pic2?
2) Which circuits are final here if a customer will turn on Circuit 0?
3) Customer can turn on circuits randomly e.g. 1-5, 1-2-3, 2-5-0. Then all circuits should be counted as final, and therefore 1.8 diversity factor should be applied to counting?
In that case:
Maximum demand = (2140W/230V*1.8(A1(Note 2)) * 0.66(A2) = 11.05A
Voltdrop (Reference method A)= (7.3*11)/1000*84=6.77V
Therefore, 6mm2 cable should be used. But it's quite costly, isn't it?
View attachment 25128View attachment 25129
wires will be buried in the ground.
Thank you.