S

sl1210

I went to see a job today where the garden gu10 spike lights trip out the rcd after an hour. i done an insulation resistance test from the switch and was getting a short between line and earth.

All the spikes and connecter boxes look ok and can't see any signs of water getting in. I disconnected the right hand side lights to see if i could narrow down the fault, and it tripped at some point again after i left. It has an rcd weather proof fusebox in the garden which seems to come of an rcd off the main house fusebox. now i've heard 2 rcd's could counteract each other, but it can't be this as they have worked fine for 19 months.

Strange thing is when i tested a couple of the lights individually with the lamps removed i was getting readings of 0.44 mega ohms line to earth, 0.55 mega ohms neutral to earth and 0.26 mega ohms line to neutral with the lamps removed. is this right for these lights? as i tested about 3 or 4 and most were giving this low readings.

Got to go back at some point and rectify this. Really baffling my brain.

Cheers
 
You've either got water ingress on the JB's or a cable damaged somewhere. What's the cable type and installation method?
 
How's the armoured run, buried, surface, clipped etc. Just laid under paving slabs, sharp stones etc can damaged the cable.
 

Reply to Garden Lights Tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
702
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Any electronics in circuit that might be skewing the readings? Smokies. Or smart switches? Might have been covered already, but what about...
2
Replies
25
Views
622
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
430

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top