Peter Woodford

Guys,

have been to look at a job tonight and the client wants a weatherproof socket installed around 20metres down his garden. Cannot dig out ground as trees flowers in way but can clip to fence. As for the length of the run would i need to run a 4mm swa or a 2.5mm Always get a bit lost on this sort of thing,need to get back into working this stuff out myself. this will be spured off of a socket down stairs . Have gave the guy a option of updating board as well or will have to fit RCBO onto board. Does any one know roughly how much a wylex RCBO is? am hoping he will go for the updated board.

Also saw in his house a switch under the stairs that should be replaced and a security light outside that did'nt have a cover over it that should be replaced was going to do this for free if he goes for the fuseboard replacement

your thoughts please
 
Hi Peter. A couple of thoughts...

Have a good hard look at that fence before you go cleating swa to it - i`ve done this before, but only when it was the most sensible option & only when i`ve critically assessed the condition of the fence as being in sound condition & likely to give many future years service.
Otherwise, i would suggest you exhaust all other possibilities.
I`m fairly sure the NIC take a dim view of this in general. Have heard they`ll even sanction a code 2 against it :eek: - but to be fair, that may be only if fence is in poor condition :(???

Are you with the NIC ? if so maybe look for guidance from them...

As for the RCBO - good idea in principle but you may struggle to source a Wylex B-curve - most of theres are C`s. Problem then would be permitted Zs halfed :eek:
Would hurt you worse if the run is a long one.
Did you take a loop measurement at feed skt? Radial or RFC? Protective device - altho i`m guessing you`ll FCU spur down to 13A?
 
ive picked up wylex rcbos for under 30 quid. as for working for free you must be joking!!
 
Remind me what op is having a bad day. Would 2.5 be o.k

tis you Peter, tis you...

OP = original poster ;) Oh dear, you are having a bad day :D

As to the cable sizing, happy to help but would need more info...cct details, protective device, Zs readings etc. but a starting point would be that 2.5mm would add approx 0.3 ohms to your existing Zs values without using the armour as additional cpc - & obviously somewhat less if you did.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Garden power
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
Peter Woodford,
Last reply from
electricAl,
Replies
8
Views
1,368

Advert

TrueNAS JBOD Storage Server

Back
Top