If these MCB's are both Type C, then i would check your Zs complies to be on the safe side!!
Don,t have access to an appropriate test meter for ZS anymore, I will replace these to type B to make sure, cheers.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss garden shed supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
If these MCB's are both Type C, then i would check your Zs complies to be on the safe side!!
Of corse because its a ring the shed feed is a radial i think ccc for 4mm clipped direct is 37amps so well with in size.
It's not a radial...it's a spur,and you can spur off a ring in 2.5mm.
Whatevers on the end it's a spur if it's connected directly to a ring.
A radial is a linear circuit connected to its own OCPD at the CU.
spurring off a 2.5mm rfc in 4mm is close to extending the rfc, like a reverse lollipop circuit. as long as the OCPDs in the shed are selected to protect the cable, can'r really see a problem with how it's been done.