It's not a radial...it's a spur,and you can spur off a ring in 2.5mm.

but is a DB classed as a spur ? i can understand a socket or a SFCU would be okay as its not possible to overload the cable with one of these

but with a DB you could quite easily pull more than the rated current of the cable if it was fed by a 2.5mm
 
spurring off a 2.5mm rfc in 4mm is close to extending the rfc, like a reverse lollipop circuit. as long as the OCPDs in the shed are selected to protect the cable, can'r really see a problem with how it's been done.
 
Only issues would be voltage drop, EFLI and overloading one point of the ring. First and last shouldn't be an issue as he has used 4mm and the load is pretty small. I'd be interested to know how the Zs stack up though.

Edit: Mind you,he has the CPC and armour of the SWA in play, so would probably be OK. :)
 
spurring off a 2.5mm rfc in 4mm is close to extending the rfc, like a reverse lollipop circuit. as long as the OCPDs in the shed are selected to protect the cable, can'r really see a problem with how it's been done.

I'll have to remember that one, ....A reversed lollipop circuit!! I like it!! lol!!
 

Reply to garden shed supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
114
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
910
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Thank you so much for that! When I went to do the Ze at the DB, I tripped the RCD in the CU in the house, I understand that's a hard question...
Replies
2
Views
262

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top