£££sjim

I have a question.How do I get the Ze for my shed ? do I get it at the intake to the small consumer unit inside my shed then do the usuall Zs= Ze + (R1+R2)The source of supply is from a socket in the garden that is direct from the house CU RCD protected. or would I have to use the Ze from the house intake position. My shed is stand alone with a light circuit 6amp mcb and two radial circuits 20amp mcb all protected by RCD. another problem I have is if the shed CU trips the house Cu trips too. both protected by 30ma RCDs the garden sockets are 32amp mcb.
 
All you need to do is as you have said measure your r1r2 then Ze at the board of the main house then Zs at the shed board can be done by calculation r1r2 + ze = Zs as its taken from a circuit at the house db it will be Zs not Ze . and the RCD's are not in series they will be in parallel
 
All you need to do is as you have said measure your r1r2 then Ze at the board of the main house then Zs at the shed board can be done by calculation r1r2 + ze = Zs as its taken from a circuit at the house db it will be Zs not Ze . and the RCD's are not in series they will be in parallel

Thanks for the sensible reply. That's what i thought but thought maybe just maybe!
 
well, i've got 2 RCDs in series on one of my jobs. it's a stables layout and i'd hate to see a horse die if 1 RCD failed to trip. so there.!
...If you really care,they would both have to be 10 Ma,as they seem to knack if you walk briskly across a nylon carpet,and pat the boogers...:stooge_curly:
 
All you need to do is as you have said measure your r1r2 then Ze at the board of the main house then Zs at the shed board can be done by calculation r1r2 + ze = Zs as its taken from a circuit at the house db it will be Zs not Ze . and the RCD's are not in series they will be in parallel[/QUOTE]

I have to disagree with you:

"The source of supply is from a socket in the garden that is direct from the house CU RCD protected. or would I have to use the Ze from the house intake position. My shed is stand alone with a light circuit 6amp mcb and two radial circuits 20amp mcb all protected by RCD. another problem I have is if the shed CU trips the house Cu trips too. both protected by 30ma RCDs the garden sockets are 32amp mcb"

????
 
What trip current are those RCDs?

they are both 30mA. the situation arose when the stables sub-main was installed with a 30mA RCD and no RCD protection at the supply end of the SWA. the main board was upgraded to RCD protected when some sockets were added to it. as there have not been any tripping issues for 3 years, i decided to leave well alone.
 
To the Op your Ze at your shed is the Zs of your sub circuit some call it Zdb the only place you find Ze is the(Origin)
so Ze + ( R1+R2 Sub Main) this is your( Ze,Zdb, Zs) for the sub board then if you want the whole Zs then add (R1+R2 Final circuit)

Hows that clear as mud lol
 
They are still in parallel L and N are the same where ever it comes from even if the supply is fed off the sockets its still Live and neutral , if it was in series then the live would enter the first rcd come out of the neutral of that RCD as a live to the live of the next RCD and the neutral would be connected to the last RCD,

[ElectriciansForums.net] garden shed Ze
 
They are still in parallel L and N are the same where ever it comes from even if the supply is fed off the sockets its still Live and neutral , if it was in series then the live would enter the first rcd come out of the neutral of that RCD as a live to the live of the next RCD and the neutral would be connected to the last RCD,

View attachment 25957
Nick I think you may have misunderstood the point, 2 RCDs on the same leg of a circuit is not recommended unless some form of discrimination has been applied, perhaps with using a time delay RCD or 2 of differing mA ratings.
I get the impression you are trying to make a point about the difference between Series and Parallel, most of us know the difference.
 
They are still in parallel L and N are the same where ever it comes from even if the supply is fed off the sockets its still Live and neutral , if it was in series then the live would enter the first rcd come out of the neutral of that RCD as a live to the live of the next RCD and the neutral would be connected to the last RCD,

View attachment 25957

So its Ok to have 2 RCD's in series then? I'm obviously missing your point.

The socket circuit supplying the shed is protected by a 30mA, then the shed has a 30mA RCD in it??

Thats how I read the OP
 
Nick I think you may have misunderstood the point, 2 RCDs on the same leg of a circuit is not recommended unless some form of discrimination has been applied, perhaps with using a time delay RCD or 2 of differing mA ratings.
I get the impression you are trying to make a point about the difference between Series and Parallel, most of us know the difference.

Yes Pete i fully understand this and im not misunderstanding the point but when it is referred to as series it is incorrect ,they are in parallel simple as , and im not having a jab at any one, its just something that keeps cropping up and just wanted to point it out , any way every one nit pic's my posts so its my turn Lol
 
Yes Pete i fully understand this and im not misunderstanding the point but when it is referred to as series it is incorrect ,they are in parallel simple as , and im not having a jab at any one, its just something that keeps cropping up and just wanted to point it out , any way every one nit pic's my posts so its my turn Lol
I wasn't nitpicking mate just trying to clarify
 
I know mate didnt think for a moment you where , archi they are still in parallel regardless of if they are a load or not lives are connected to lives neutrals to neutrals that is parallel
 
I know mate didnt think for a moment you where , archi they are still in parallel regardless of if they are a load or not lives are connected to lives neutrals to neutrals that is parallel

ha ha, I see your point!

I still say having 2 x 30mA RCD's on the same circuit is bad practice - whether they be parallel or series!!
 
I know mate didnt think for a moment you where , archi they are still in parallel regardless of if they are a load or not lives are connected to lives neutrals to neutrals that is parallel

OK, they're not electrically in series, L & N are effectively electrically separate, but you could argue they are magnetically in parallel! :)

Me and everyone else will keep refering to them as being in series.
 
Agree they are in series remove or trip the first and the second is dead in parallel it would still be energised. Either one or both may trip in fault conditions therefore no discrimination is the point that being made.
If the feeds were in parallel only the the one with a fault would trip

[ElectriciansForums.net] garden shed Ze
 
Yes Pete i fully understand this and im not misunderstanding the point but when it is referred to as series it is incorrect ,they are in parallel simple as , and im not having a jab at any one, its just something that keeps cropping up and just wanted to point it out , any way every one nit pic's my posts so its my turn Lol

The coils of the RCD are in series rather than parallel, the current passes through the first live coil, then the second, then the second neutral coil then the first ;) ;)
 

Reply to garden shed Ze in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Thank you for another very helpful response. Just to assure you we are saying the same thing, I was referring to the 2.5 on 20A radial which I now...
2
Replies
25
Views
2K
Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
541
  • Question
Do you know what percentage of scheme registered electricians are registered to sign off 3rd party work? Even better would be a poll of how many...
2
Replies
25
Views
2K
nicebutdim
N
  • Question
It’s all a bit confused as he originally says I read that as with supply removed he was picking up 230v. My concern is/was that as the house...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks