Hi All,
Detached house, about 15 years old, on an estate. Customer wants a socket and some light on his decking area at the end of the garden (for amenity, not security). It's bordered on two sides by brick walls (one is next door's garage).The easiest source is from his detached garage (supplied by a very short existing underground run from the CU in the house).
TN-C-S supply. Garage supply on 30A MCB on RCD side of CU in house (shared with kitchen sockets!). All other socket circuits are also on this single RCD.
Garage has 2 way CU, 16A sockets, 6A lights. No spare ways in either board.
I'm intending to take the garden supply via a SFCU with 13A fuse off the garage sockets circuit. Through wall to plastic adaptable box. 3 core 2.5mm² SWA, 30m long, down wall and underground to MK masterseal double socket on wall by decking. Short conduit link to double pole masterseal switch for lights. 1.5mm² HiTuf or NYY-J clipped to wall to each light (3off ?).
Any earth fault in the garden will trip out all the house sockets; not ideal but that's how it is. 2.5mm² is ok for, say, 2.5kW load (eg large garden power tool) and still be OK for VD on lights. 2 core SWA would be slightly cheaper, but I like the security of one core for the CPC. Not measured Ze yet, but it would have to pretty high for the Zs not to be OK.
The underground cable run will be in a narrow strip of gravel between the brick wall and a slab path. No digging likely but as it'll only be a few inches down, I'm inclined to supply a piece of
polythene cable duct for the customer to bury and then I can pull the swa through when he's done.
Any comments generally?
In particular on the supply to the lights being protected by the 13A fuse in the SFCU? I think it's OK. The cable rating is higher than this; it's only the wiring inside the lights (whatever they end up having) that may be a problem, but it's a small fixed load.
Does anyone know of some nice looking bulkhead lights or maybe some wall mounted spots that will take a surface run cable? Most domestic lights are designed only for back entry, which is not possible in this case.
Detached house, about 15 years old, on an estate. Customer wants a socket and some light on his decking area at the end of the garden (for amenity, not security). It's bordered on two sides by brick walls (one is next door's garage).The easiest source is from his detached garage (supplied by a very short existing underground run from the CU in the house).
TN-C-S supply. Garage supply on 30A MCB on RCD side of CU in house (shared with kitchen sockets!). All other socket circuits are also on this single RCD.
Garage has 2 way CU, 16A sockets, 6A lights. No spare ways in either board.
I'm intending to take the garden supply via a SFCU with 13A fuse off the garage sockets circuit. Through wall to plastic adaptable box. 3 core 2.5mm² SWA, 30m long, down wall and underground to MK masterseal double socket on wall by decking. Short conduit link to double pole masterseal switch for lights. 1.5mm² HiTuf or NYY-J clipped to wall to each light (3off ?).
Any earth fault in the garden will trip out all the house sockets; not ideal but that's how it is. 2.5mm² is ok for, say, 2.5kW load (eg large garden power tool) and still be OK for VD on lights. 2 core SWA would be slightly cheaper, but I like the security of one core for the CPC. Not measured Ze yet, but it would have to pretty high for the Zs not to be OK.
The underground cable run will be in a narrow strip of gravel between the brick wall and a slab path. No digging likely but as it'll only be a few inches down, I'm inclined to supply a piece of
polythene cable duct for the customer to bury and then I can pull the swa through when he's done.
Any comments generally?
In particular on the supply to the lights being protected by the 13A fuse in the SFCU? I think it's OK. The cable rating is higher than this; it's only the wiring inside the lights (whatever they end up having) that may be a problem, but it's a small fixed load.
Does anyone know of some nice looking bulkhead lights or maybe some wall mounted spots that will take a surface run cable? Most domestic lights are designed only for back entry, which is not possible in this case.