Metal shed In Garden with no extraneous conductive parts
House electrics PME supply
Garo make a 40a PME fault detection unit for EVs and I was thinking of exporting the PME via the garo init at the supply end and swapping out the factory 30ma to a 100ma time delay
Then use 30ma RCBOs in the final circuits, reason being is I don’t like using TT rods and relying on RCDs as the means of ADS as they always become locked up over time.
The garo unit seems to be a sound way to protect the shed supply in the event of a PME fault and I get to use a superior earthing system
What are your thoughts