Gas and water main bonding

Hi,

I have a submain 16mm t+e and separate 10mm, question is submain comes from cellar up to ground floor, gas meter is next to incomer in cellar and water stoptap is other end of property....gas will be bonded to met at incomer but is it ok to bond water back to consumer unit on ground floor as this has a 10mm already going back.

i believe it is ok, or do the main bonding conductors always have to go back to 1 met or can it be done (which I believe it can as if you have a submain going out to an outhouse you can have combined earth and bonding conductor if extraneous parts are present)

I just can't remember if you can have only one met or not as I wouldn't normally do it this way lol

thanks
 
There is only one MET, by definition.
However it is possible (but not recommended) to have a joint in a bonding conductor (e.g in a consumer unit, joined by an earth bar!), it is normal to ensure that the bonding conductor cannot be inadvertently disconnected so it should be clear what is happening, e.g. have the two conductors in adjacent bonding conductor terminals.

This is not an ideal situation however it is a practical and permitted solution.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
Jdsparky,
Last reply from
Richard Burns,
Replies
1
Views
1,211

Advert

Back
Top