A customers gas meter is in the kitchen approximately 12m away from the Met which is located in the hall.

The suppliers wont change the gas until an earth is present.

I can get a cable to the meter part externally and internally, total cable length 12m, whilst i was there the guy from the supplier seems to think this is not acceptable and the bond needs to be were the pipe comes into the house?

I Thought that bonding conductor should be within 600mm of the service meter on the consumers side or at the point of entry into the building ?

Advice please.
 
So what happens if there is a junction in the gas pipe, close to the meter, a few meters from the entry point to the dwelling then?

As all gas pipes are continuous copper I think if you tested continuity between the point where you should bond and the point where you do bond you'll get a value below 0.05 ohms.

See page 41 of the OSG. Table 4.4(ii) note iii with reference to reg 544.1.2.
Where practicable, the connection to the gas, water, oil, etc, service should be within 600 mm of the service meter, or at the point of entry to the building if the service meter is external and must be on the consumer's side before any branch pipework and after any insulating section in the service.
Hence this implies that the 600 mm rule is for internal meters. Other than that, regarding your question, you're the professional you decide!
 
600mm after the meter on the consumer side, before any junctions in the pipework, and importantly "where practical".

Make sense of that!

Yep I have noticed that is some flats they are putting the meter at ground level for the meter reader but they run the supply pipe up the external wall so is it 600mm from the meter and that means running the earth outside or is it 600mm as it enters the property me thinks the later but as always these gas safe guys are told 600mm at the meter and thats it
 
and that means running the earth outside or is it 600mm as it enters the property me thinks the later but as always these gas safe guys are told 600mm at the meter and thats it

From Viper, a Gas bible;

The cross bonding clamp should be attached to the carcass pipe not more than 600mm from the meter (internal meters).
For meters located in outside meter boxes the cross bonding should be inside the building as near a practicable to the point of entry of the installation pipe.
The bonding may be attached within the meter box providing the integrity of the meter boz or any sleeving is not compromised.
 
Boilers
I hear those nightmare words echoing again,"Manufacturers instructions"

Of course you are right,that is until the gas guy opens his book and sees an instruction to bond them,you are then trumped

All the classroom instruction and years of design and installation you may have undertaken, has to be thrown aside, because some Japanese scriptwriter who can't speak English like us "tidy"Welsh people ,inserts his drivel

The regs should be amended as soon as,to redress this issue

Well I had a foot in both camps as both a Spark AND Gas Fitter, so if I was installing a boiler, I would bond ALL the pipes under the boiler, but if I was attending in my capacity as a spark, I wouldn't.

(and they wonder why I'm a bit schizophrenic)
 
Im a Pit Yakker! not a bloody mac"scum".............. Durham Coal Fields Born and Bred.... i remember the winding gear, i remember the coal train... mind you had to go to easington to see it.... family of miners not half built shipyard workers with nee keeys...!

we used to be friends...!
 
Im a Pit Yakker! not a bloody mac"scum".............. Durham Coal Fields Born and Bread.... i remember the winding gear, i remember the coal train... mind you had to go to easington to see it.... family of miners not half built shipyard workers with nee keeys...!

we used to be friends...!

Sorry bonny lad - I meant no harm - but it's BRED (as in breeding) not BREAD (as in what ye dip in yer gravy)..... only a Mackem would confuse the two ;)
 
I thought the 600mm rule was only for internal meters. Otherwise it's as close as practicable to the point of entry to the property.

I agree, it complies with BS7671 and gas regs.

Meter inside the property, then within 600mm of the meter before any Tee or branch.

Meter outside then within 600mm of the point of entry.
 
i did some apartments point of entry in each apartment was at the boiler the gas meters were in the carpark basement so i bonded at the boilers as that was my point of entry in the apartment and that is where the potential could be, the plumbers wanted the meters bonded or else they wouldnt sign off the new install.i ended up bonding them but i got paid to do it.
 
i did some apartments point of entry in each apartment was at the boiler the gas meters were in the carpark basement so i bonded at the boilers as that was my point of entry in the apartment and that is where the potential could be, the plumbers wanted the meters bonded or else they wouldnt sign off the new install.i ended up bonding them but i got paid to do it.

I had a similar situation recently so called NICEIC Tech helpline who said bond the gas as close as possible to where the pipe enters the flat
 

Reply to Gas Meter earth in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
411
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
669
loz2754
L
I like your way of thinking.
Replies
6
Views
631
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top