Evening All,
Another bit of advice please.
Doing a property at the moment and it has no bonding on the gas pipe.The problem is I have
electric meter box one side of house and Gas meter box the other.I know I have to bond with 10mm and within 600mm of gas meter on consumer side.But this means i have to run an unsightly cable around half of the whole house !.The boiler is within a couple of feet of the dual RCD protected CU and the gas feed to that comes down from the roof in a loft which has no access.Bonding to water services measures 0.02 as it so close ,so that good.
Its a TN -C -S and measured Ze is 0.36 and apart from some crazy IR readings as a result of additions over the years with bits in cupboards and still looking and not being able to isolate things the house seems ok.All my Zs readings will come within spec.
Could I not bond at the nearest available point ie where the gas pipe comes down from the ceiling near the CU and close to the bolier,althought it has branched off to feed a gas fire before that point.
I guess my Zs will drop when bonded but how much do I gain ?
Whats the opinions of the wise forum ? I am sure I am not the only one to have come across this one.I know what the OSG says and the BRB does say 'practicable' but come judgement day.
Thank you
Another bit of advice please.
Doing a property at the moment and it has no bonding on the gas pipe.The problem is I have
electric meter box one side of house and Gas meter box the other.I know I have to bond with 10mm and within 600mm of gas meter on consumer side.But this means i have to run an unsightly cable around half of the whole house !.The boiler is within a couple of feet of the dual RCD protected CU and the gas feed to that comes down from the roof in a loft which has no access.Bonding to water services measures 0.02 as it so close ,so that good.
Its a TN -C -S and measured Ze is 0.36 and apart from some crazy IR readings as a result of additions over the years with bits in cupboards and still looking and not being able to isolate things the house seems ok.All my Zs readings will come within spec.
Could I not bond at the nearest available point ie where the gas pipe comes down from the ceiling near the CU and close to the bolier,althought it has branched off to feed a gas fire before that point.
I guess my Zs will drop when bonded but how much do I gain ?
Whats the opinions of the wise forum ? I am sure I am not the only one to have come across this one.I know what the OSG says and the BRB does say 'practicable' but come judgement day.
Thank you